[Equest-users] reheat fan system
David S Eldridge
DSE at grummanbutkus.com
Mon Dec 15 13:50:59 PST 2008
Marcus, if your min-flow-ratio is zero, the simulation will allow VAV box to completely close as the cooling load for the zone becomes smaller. Conversely, if you set the value to 1.0, then that zone will operate in constant volume.
This may not be your intent as the zone wouldn't be receiving any ventilation under the "min-flow-ratio = small" conditions, and the heating energy would be expected to be large if "min-flow-ratio = 1.0" as the zone would be constant volume with reheat.
Your as-built/proposed design VAV boxes may be selected to partially close to maintain a minimum CFM/SF and/or per person, at which point reheat might be added to maintain temperature control in the space while still providing ventilation. I noticed that your AHU has a minimum flow ratio of 0.2, so the intention seems to be that on average the zones would add up to a weighted average of about 0.2 also. (I don't believe these have to be the same, the higher quantity would set the amount.)
David
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-
> bounces at lists.onebuilding.org] On Behalf Of Marcus Eliason
> Sent: Monday, December 15, 2008 2:03 PM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] reheat fan system
>
>
> Hello,
>
> I have been working on a building that I am modeling with a reheat fan
> system. My question is about the MIN-FLOW-RATIO. It seems that my heating
> energy for the building is directly tied to this number. When, I put the
> ratio near zero, my heating energy is nonexistent and is quite large when
> the ratio is set to 1. I have attached a sample for reference. Can
> someone explain what might be happening, because I don't believe the
> heating energy results the simulation is giving me?
>
> Thanks,
>
> Marcus Eliason
More information about the Equest-users
mailing list