This is crankcase heat which defaults to 50 w.  Thanks for all the
responses!!  I still don't understand why there is more crankcase use in the
colder months, but I am all set for now.
Thanks!
--
Karen
On Wed, Jul 23, 2008 at 5:46 PM, Kevin <kevinjm5000 at yahoo.com> wrote:
> I believe this is crank case heating (SYSTEM:CRANKCASE-HEAT) which defaults
> to 50 Watts (0.050 kW) for PVVT with an on temperature (CRANKCASE-MAX-T) of
> 50. If you set CRANKCASE-HEAT to zero, I think this energy goes away.
> - Kevin
>
> --- On *Wed, 7/23/08, Karen Walkerman <kwalkerman at gmail.com>* wrote:
>
> From: Karen Walkerman <kwalkerman at gmail.com>
> Subject: [Equest-users] DX units result in "Pump & Aux" energy use
> To: equest-users at lists.onebuilding.org
> Date: Wednesday, July 23, 2008, 2:13 PM
>
> Hi All,
>
> I'm working on a project where I have a system type of "PVVT" specified.
> When I have air-cooled DX units specified, my "Pump & Aux" energy goes WAY
> up (about 4500 kwh are attributed to pumps and 19000 kwh attributed to
> something having to do with the DX units).  The SS-P cooling summary report
> shows some sort of energy use for each unit every month, even when there is
> no cooling load.  Curious thing, is that the highest loads are in the
> winter.  I always result in 37.6kwh used in jan, 33.6 in feb, etc.  I also
> ran a test module straight from the wizard with a PVV system.  The system
> size is much larger, and it still uses... 37.6 kwh in jan, 33.6 in feb (the
> other months there is a cooling load).  Any idea where this comes from or
> how to make it go away?  The DX units will be OFF in the winter.  It seems
> that the program is simulating some sort of heating for the DX unit.
>
> Any thoughts?
>
> Thanks,
>
> --
> Karen
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080723/ca34fe6a/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list