[Equest-users] [Bldg-sim] Scroll Chiller
Fred Porter
FPorter at archenergy.com
Mon May 19 16:51:00 PDT 2008
The eQuest library contains a curve set for an air-cooled scroll chiller. There is no indication if this represents multiple compressors or not, but if you compare the EIR-fPLR curve outputs w/other chillers you might be able to tell. These curves would be selected from the custom curves list in the chiller window / performance curve tab in eQuest, then from each drop down, "library" -> "chiller," after which the curve appears.
Otherwise the multiple-compressor "reciprocating" chiller curves might provide a reasonable representation of typical scroll chillers, at least w/o the effort of making custom curves. These are selected by eQuest automatically when the user selects the "type" & compressors/ckt from the main chiller window. Check the default minimum cycling and hot gas bypass ratios.
----- Original Message -----
From: Eric Youngson
To: bldg-sim at lists.onebuilding.org
Sent: Monday, May 19, 2008 12:47 PM
Subject: [Bldg-sim] Scroll Chiller
SIM List,
I need to model a scroll chiller (. Does anyone have an opinion on which eQUEST chiller is a reasonable choice for this? I was thinking that centrifugal would be the closest but this is simply based on mechanical operation. I would like to choose the closest model based on performance.
Eric Youngson PAE Consulting Engineers, Inc. 503.226.2921 Main
503.542.0567 Direct
503.226.2930 Fax
ericy at pae-engineers.com
Mechanical 808 SW Third Avenue - Suite 300
Portland, OR 97204-2426
www.pae-engineers.com
inspire interpret integrate
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080519/c281ae6a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2029 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080519/c281ae6a/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 143 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080519/c281ae6a/attachment.png>
More information about the Equest-users
mailing list