[Equest-users] Combining Parametric Components

Vikram Sami VSami at lasarchitect.com
Mon Jun 1 14:27:10 PDT 2009


Actually when you run parametrics cumulatively I believe they do take the properties of the previous run into account. So for example if run#6 makes your glass darker and run#7 adds daylight sensors, run#7 will assume the darker glass.  

Vikram Sami, LEED AP 
Direct Phone 404-253-1466 | Direct Fax 404-253-1366 
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361 
Responsive Design • Technological Expertise • Exceptional Service 
Please visit our new website | www.lordaecksargent.com
Think GREEN before you print.


-----Original Message-----
From: John Aulbach [mailto:jra_sac at yahoo.com] 
Sent: Monday, June 01, 2009 5:21 PM
To: Jeremy McClanathan; equest-users at lists.onebuilding.org; Vikram Sami
Subject: Re: [Equest-users] Combining Parametric Components


Jeremy, What Vikram says is correct. However, I believe you STILL need to add all of the Parametric components into one run to compare to the Base. Run #7 will compare to Run #6, but Run #7 won't have Run #6 parameters in it, as well as its own. 

In other words, the parameters will not accumulate as the run numbers get bigger. I believe you still need a cumulative run will all envelope parameters added into that run.

John Aulbach

--- On Mon, 6/1/09, Vikram Sami <VSami at lasarchitect.com> wrote:

> From: Vikram Sami <VSami at lasarchitect.com>
> Subject: Re: [Equest-users] Combining Parametric Components
> To: "Jeremy McClanathan" <jmcclanathan at CDiengineers.com>, equest-users at lists.onebuilding.org
> Date: Monday, June 1, 2009, 2:09 PM
> 
> 
> 
>  
>  
> 
> 
> 
> 
> 
> 
>  
> 
> 
> 
> You can
> run the parametric runs
> incrementally or cumulatively.  To run them
> cumulatively, in the parametric
> run dialogue, you need to base the run on the previous run
> (you can base the un
> on any parametric run preceding it).  
> 
> 
>   
> 
> 
> 
> Vikram
> Sami, LEED AP 
> 
> Direct
> Phone 404-253-1466 | Direct Fax 404-253-1366  
> 
> LORD, AECK & SARGENT ARCHITECTURE
> 
> 1201 Peachtree Street NE, Suite 300,
> Atlanta, GA 30361 
> 
> Responsive
> Design · Technological Expertise · Exceptional
> Service 
> 
> Please
> visit our new website | www.lordaecksargent.com 
> 
> P
> Think
> GREEN before you print. 
> 
>    
> 
> 
> 
> 
>   
> 
> 
> 
> 
> 
> From: equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] On
> Behalf Of Jeremy
> McClanathan
> 
> Sent: Monday, June 01, 2009 4:57 PM
> 
> To: equest-users at lists.onebuilding.org
> 
> Subject: [Equest-users] Combining Parametric
> Components 
> 
> 
> 
> 
> 
>    
> 
> Hello, 
> 
>    
> 
> Does anyone out there know whether or
> not it is possible to
> take parametric components that are currently each being
> used for individual
> parametric runs and combine all of them under 1 parametric
> run? 
> 
>    
> 
> Currently, I have a model where I have
> analyzed 13 envelope
> measures using parametric runs.  Now, I would like
> combine all of them
> into 1 run called envelope measures.  Is this
> possible? 
> 
>    
> 
> Jeremy 
> 
>    
> 
> This email message, including
> any attachments, is for the sole use of the intended
> recipient and may contain
> confidential, proprietary, and/or privileged information,
> as well as content
> subject to copyright and other intellectual laws.  If
> you are not the
> intended recipient, you may not disclose, use, copy, or
> distribute the email
> message or its attachments.  If you believe you have
> received this email
> message in error, please contact the sender by reply email,
> immediately delete
> this email and destroy copies. 
> 
> 
> 
>  
> 
> 
> 
> -----Inline Attachment Follows-----
> 
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank
> message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> 


      



More information about the Equest-users mailing list