[Equest-users] Strange errors in file- HELP!
Carol Gardner
cmg750 at gmail.com
Fri Jul 9 10:32:58 PDT 2010
Hi Paul,
Here's my strategy when this happens to me. I open the *.inp* file and the *
.bd*l file in Word. I then use the Edit, Find feature and search on ERROR in
the *.bdl* file. When I find the line that the error is occurring in I then
fix it in the *.inp* file. Repeat until all errors gone. You probably have
an existing space that shared an interior wall with your now deleted space
and is trying to reference it using" NEXT-TO". Be sure to fix the error in
the *.inp* file not the .bdl file, which I have done a few times. This is
one example of why it is good to familiarize yourself with the Building
Descriptive Language (BDL): you can make these sorts of fixes much easier in
your input deck using than trying to figure it out in DD edit. Just be sure
not to delete any delimiters (..)
Let me know how you do..
Carol
On Fri, Jul 9, 2010 at 8:33 AM, Paul Brooks <equestpaul at yahoo.com> wrote:
> I am modeling an addition to an existing building. I originally did the
> shell/zoning using just the original building. I then, after saving a back
> up copy of the base building, i went back to the shell and zone drawing
> screens in the DD wizard and expanded the shell to account for the addition,
> and then went into the zone creation and adjusted my zones. I was sure to
> follow the rules about matching verticies, etc.
>
> Now i am getting errors concerning the zone and plenum. It appears that
> the program is still seeing plenums and walls that are now non-existent.
> The program says that plenums are being referenced but are not defined (see
> error message below).
>
> Anyone got any ideas on how to clear this?
>
>
>
>
>
>
>
> *ERROR****************************************************************************************
>
> *ERROR*****EL3 East Perim Plnm (G.E6) was referenced on line 14898 but
> never
>
> defined.
>
>
> *ERROR****************************************************************************************
>
> *ERROR*****EL3 West Perim Spc (G.W4) was referenced on line 15237 but never
>
> defined.
>
>
> *ERROR****************************************************************************************
>
> *ERROR*****EL3 WNW Perim Plnm (G.WNW7) was referenced on line 15377 but
> never
>
> defined.
>
>
>
>
>
> **************************************** 5 ERRORS
>
> **************************************** 2 WARNINGS
>
> **************************************** 103 CAUTIONS
>
> *20195* COMPUTE ..
>
> *20196* STOP ..
>
> **************************************** 5 ABORT-LEVEL DIAGNOSTICS
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/568892ae/attachment-0001.htm>
More information about the Equest-users
mailing list