[Equest-users] LEED EAp1 baseline problem
Jenny Zhang
jenny.zhang at arup.com
Thu Aug 25 19:36:31 PDT 2011
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of 何宗翰
Sent: 2011年8月26日 9:07
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED EAp1 baseline problem
Hello All,
I am trying to establish the baseline model for LEED NC 3.0, and have some problem as following:
1. From ASHRAE 90.1 2007 G3.1.2.8, does it mean that I can simulation the supply airflow rate by
setting MIN-SUPPLY-T & DESIGN-COOL-T have 20 degree difference and let eQUEST to calculate the
supply airflow automatically? YES
2. My baseline HVAC is system No.8, VAV with PFP boxes, so from G3.1.3.12, the supply air temperature reset must depend on the load, but I can't find this setting option in eQUEST, could anybody tell me how to set that? you could find reset setting options on the ‘air side system’>system>cooling>control and reset.
3.Because I am not in a LEED project, could anyone send me the LEED NC3.0 "EAp2 Section 1.4 table.xls" to check if there is anything I loss? please see the attached file, also you could down it on LEED online Credit Resource.
Thanks in advance,
Stan Ho
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110826/f5a3f7ef/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EAp2 Section 1.4 tables.xls
Type: application/vnd.ms-excel
Size: 51712 bytes
Desc: EAp2 Section 1.4 tables.xls
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110826/f5a3f7ef/attachment-0002.xls>
More information about the Equest-users
mailing list