[Equest-users] eQuest - Exhaust Fan Schedule
Nick Caton
ncaton at smithboucher.com
Mon Feb 14 09:53:40 PST 2011
How I handle exhaust like this varies from project to project..
As a preface, the easiest/simplest way to handle any exhaust that draws air from another conditioned space is to define an exhaust CFM and schedule on the system from which the conditioned air is being drawn, or at the space the air is being drawn from (I don't believe the exact location where you define the exhaust is critical, but it helps you/others understand what you were doing after the fact) - as a corollary I usually call such spaces without conditioned supply air 'unconditioned' spaces in modeling terms. This approach however funnels you into using a fractional or on/off schedule. This may be perfect if your exhaust is 24/7, running on a fixed schedule via BAS or timeclock, or tied to the restroom lights (just use the light schedule).
If/when you want the exhaust to run off a space thermostat temperature, I don't think you have any alternative but to define a system for the space(s) involved, as Rob is getting at. I'd suggest the simpler approach above unless you have time to spare or want to know a "righter" way to approach the issue ;). There's multiple ways to skin this cat in eQuest...
I'd suggest starting with a PTAC:
· make it CV,
· zero out its cooling EIR (the cooling is "free" being drawn from elsewhere),
· remove any heating element that may be there by default (not sure without looking)
· set its min supply temp to match the conditioned space temp being drawn in,
· input fan energy (kW/CFM) to match the exhaust fan(s) - zero out the temperature rise to the airstream while you're at it
· modify the space/cooling schedule thermostat setpoints to the temperature being maintained
· oh yeah - make sure the control zone matches where the thermostat resides.
That should get you in the ballpark... on further thought you might set the cooling EIR to match that of the system actually conditioning the air being drawn in - invest as much time in this as you deem necessary ;).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Monday, February 14, 2011 11:25 AM
To: David Cantrill
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest - Exhaust Fan Schedule
My initial thoughts is to model the exhaust fan as a supply fan. then set up your fan schedule to turn on only to meet space loads and create a 85 deg thermostat schedule. Then set up your system to get its outside air from another system to simulate the fact that the exhaust fan will be drawing air in from adjacent spaces. hopefully someone out there might agree or add to my initial thoughts.... (please)
hope this helps
Rob
On Mon, Feb 14, 2011 at 11:52 AM, David Cantrill <dcantrill at cxgbs.com> wrote:
I am modeling a building which uses exhaust fans in the electrical rooms. These fans are designed to be on when the room temperature is above 85°F and off when it is below. How would I set a schedule up in equest to run the fans in this manner?
Thank you,
David Cantrill
Branch Manager - Mississippi
Error! Filename not specified. <http://www.cxgbs.com/>
CxGBS is not responsible for design concept, design criteria, compliance with codes, design or general construction scheduling, cost estimating, or construction management.
CONFIDENTIALITY NOTICE: This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged. If you are not the intended recipient or the person responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone at (770) 831 6760 and destroy the original transmission and its attachments without reading them. Thank you.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110214/96792406/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110214/96792406/attachment-0002.jpeg>
More information about the Equest-users
mailing list