[Equest-users] Natural Draft Boiler G3.1.3.2
Paul Diglio
paul.diglio at sbcglobal.net
Sat Jun 18 06:02:58 PDT 2011
Magda:
Isn't the G3.1.3.2 requirement for a natural draft boiler only for the
baseline? The proposed model should reflect the as-designed heating plant.
If the boiler is oil-fired a forced draft burner is required.
Even a natural draft boiler uses some electric energy for the gas valves, stack
damper, intermittent ignition and control system.
Paul Diglio
________________________________
From: Magda Lelek <magda at andelmanlelek.com>
To: equest-users at lists.onebuilding.org
Sent: Fri, June 17, 2011 4:47:03 PM
Subject: [Equest-users] FW: LEED Review Comment - Exhaust Fans
Dear Pasha,
Regarding you criticism of the reviewer’s comments about the electric heat use
in case of your project – please note that he/she was correct. Please note
that according to G3.1.3.2 (ASHRAE Appendix G) boilers shall be “natural
draft”. Your boiler type (forced draft) was incorrect. Contrary to your
assertion the reviewer was correct and possibly merely trying to enforce
consistent standard and I actually applaud him/herfor that.
Sincerely,
M. Magda Lelek, P.E., CEM
LEED Accredited Professional
Andelman and Lelek Engineering, Inc.
1408 Providence Highway
Norwood, MA 02062
781-769-8773 tel.
781-769-8944 fax
www.andelmanlelek.com
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Friday, June 17, 2011 3:12 PM
To: Ömer Moltay
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED Review Comment - Exhaust Fans
Omer---I have your reviewer also on one of my projects...I literally just
finished the 33 comments back to the reviwer only 6 hours ago. I'm exhausted
and frustrated (hopefully I'm not alone in these feelings after fighting with
LEED & GBCI...)
I had the exact same comment, but I already had the exhaust fans in both the
baseline and proposed. I was also told to break-out the fan energy which was
annoying to have to back-track on these tedious things, add an extra meter,
etc.... I also ran into the same issue of mis-match output results and I could
not track what was the cause of it. I ended up explaining how the discrepancy
in energy is literally negligible in the whole building picture of annual energy
use. Exhaust fans and motors are small--in the sense of the ones they are
refering too and to spend a whole hour fixing, revising, and rewriting
explanations in the hopes that I appease this reviewer is EXHAUSTING and
FRUSTRATING....also this change made virtually no change or difference in my
overall results comparison as my reviewer pointed out that these fans are
considered process loads and therefore are held equal in both cases...UGH.
Further more, it ultimately feels that GBCI and the LEED Reviwers are always
"out to get us"....What's going on with the LEED Comment discussion on Assembly
U-values being unacceptable???!!! I have never had a LEED reviewer comment
about this modeling approach and I've completed LEED sims from LEED version
1.0. This is really starting to get to be tooo much of a double standard for
inconsistencies within the GBCI EAc1/EAp2 reviewers. The amount of work that
is required for the reporting is ridiculous. Why do the new forms make us
simulators take time to transpose the Appendix D climate characteristic data
from 90.1 into the LEED template....
There doesn't seem to be much support or comfort when "working for" a LEED
reviewer and to TAKE THE CAKE....several comments in my LEED review were
unprofessional on thier part AND they are incorrect! For example my LEED
reviewer takes the liberty to state: "... Table G3.1.1B indicates that the
heating type for system type 7 is hot water fossil fuel boiler only, so there
must not be any energy consumption for electric space heating. "...
The following was my response back to them where based on my 10+ yrs of
simulation & HVAC design experience warranted thier statement ignorant and
unprofessional in my opinion. Statements like this from GBCI Reviewers are
insulting to experienced simulators (maybe to inexperienced simulators too?) and
only make the LEED Reviewers look inexperienced and unknowledgable---which makes
me question thier ability to adequately review my energy models:
Response: First off it is incorrect to state, “so there must not be any energy
consumption for electric space heating.” The order of magnitude is small enough
(equalling 0.4% of the total energy use in the whole building), that the impact
of this energy is more than negligible. Thus indicating that this electric
energy usage is coming from something very small in comparison to the over all
building systems. Second, looking at the output summary document for the
simulation tool the screen shot below shows that “boiler draft fan electric use
is included under SPACE HEATING, not PUMPS & AUXILLARY EQUIPMENT.” Therefore
the small amount of electric space heating that is being reported is being
accounted from the hot water boiler draft fans.
I tested the model where this energy was coming from and found that in the
boiler input window the efficiency is represented as an HIR value, and there was
a small default input for the EIR input associated with the equipment. To
appease the confusion of this small amount of electric energy that was being
reported I have zeroed-out the EIR input value that was causing the results to
be unacceptable to the LEED Reviwer.
---end of response comment----
I don't really want to use the term "enemy" but with these types of stupid
comments from LEED EAc1 reviewers they certainly feel like the enemy who's goal
is to work against the Simulation crusade to better our design industry with
these integrated design tools and skills.
HOW CAN WE REGARD GBCI & USGBC AS INDUSTRY 'GURUS' AND EXPERTS WHEN IDIOT
COMMENTS ARE COMING FROM THE SIMULATION REVIEWERS. I certainly have lost any
amount of respect or comfort in the "expertise" of the GBCI & USGBC
organizations with regards to energy simulation for real life and for compliance
purposes.
Note to GBCI---you cannot apply a cookie-cutter approach to energy simulation
reviews, where there is literally NO cooking-cutter approach to creating energy
simulations. The EAc1 review process needes to become more dynamic and
interactive, so at the very least you can let me educate your reviewers since it
is obvious they are not getting the proper training nor does it seem they even
have any simulation experience at all to do a minimally adequate review of an
energy model.
It is my professional opinion that GBCI EAc1 Review Team is losing face quickly
amongst the greater populus of LEED simulators. At this point in time I'd
sooner start consulting to my clients that doing the formal LEED process will do
nothing for them but waste more money and cause more stress and headaches in the
long run. I'll certainly suggest that they apply the "principals" and
strategies of LEED but without the 'marketing-monopoly hype' spewing from
USGBC/GBCI lackies.
Furthermore as a LEED simulator and an Engineering Consultant there is ZERO
support from USGBC/GBCI in support of what reasonable simulation fees and costs
should be to comply with all of the ridiculous requirements that are being
mandated to be completed for EAc1. Over the years of new LEED versions, the
amount of information detail being "required" by the reviewers has increased at
least 3-fold, however I've observed that energy simulation fees have been at a
stale-mate for the past 10 years and have had no opportunity for growth--in fact
it is more likely that simulation fees have been continuously decreasing over
the years while the LEED work reqirements continue to increase.
The only thing that I get out of this LEED phenomena is more headaches...all of
my LEED projects are at a profit loss due to the amount of extra work imposed on
us by the LEED Comments and requirements of the reviewer (i.e. my comment
example above). I spent an extra 45 minutes composing that response and
verifying that I WAS CORRECT, to prove to the LEED reviewer that thier comment
was completely false in how it applied to my project. At an average hourly
simulation rate of $125/hour, this LEED comment cost me an extra $94 of time
that could have been legitimately spent working on another model that will be
useful for the client to use and help impose an industry shift towards
sustainable building design standards.
...Instead, this comment cost me an extra $94 out of my pocket to "argue" with
the LEED reviwer who virtually isn't even there or listening to me....so in a
sense I am also throwing more money towards USGBC inclusive of the
multi-thousand dollars that my client has already paid them. DEAR
USGBC---please stop raping the industry for the money monopoly that you have
created. The sense of GREED is oozing from everything that comes out of
USGBC/GBCI with a price tag on it or a cost associated with it.
(my profit loss is due to extra unforseen time expended to fulfull LEED comment
requirements beyond the fee that I had estimated to my client.)
Pasha Korber-Gonzalez
Korber Energy Consultants
www.korberenergy.com
pasha at korberenergy.com
Direct Ph: 308-763-1593
2011/6/16 Ömer Moltay <omoltay at mimtarch.com>
Dear Crina,
Thanks for the reply. I just added these exhaust fans to my baseline model. The
reviewer is also asking for a separate energy consumption calculation for the
exhaust fans. While trying to capture this through separate meters, I just
realized that the air volume exhausted through some of these independent fans is
variable in hourly reports even if I define them to be constant volume. I am
afraid that this will result in mismatching values for energy consumption
between the baseline and the proposed models.
1. What could be causing the air volume to be variable?
2. Is it a must that both the baseline and the proposed cases should display
exactly the same amount of energy consumption for these independant fan systems?
Thank you,
Omer Moltay, LEED AP BD+C, BREEAM Assessor Mimta Ltd.
Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.mimtarch.com
www.mimtasolar.com
www.eko-yapi.net
Sürdürülebilir Binalar Blog
http://surdurulebilirbina.blogspot.com/
Green Building in Turkey on LinkedIn
http://www.linkedin.com/groups?gid=2278249
14.06.2011 00:04, Bosch, Crina yazmış:
Omer,
They are talking about independent fans like toilet exhaust or kitchen exhaust.
Those values that you have under EF-1 thru EF-9 need to be equal between
baseline and proposed model. So, if you have EF-1 at 300 cfm and 2KW for that
fan, you need to input the same values in baseline model. Those fans are
separate than the Exhaust from the AHU. I usually input them at space level and
the kw/cfm for those fans.
Hope this helps.
Crina Bosch
Engineer, Mechanical
karpinski
ENGINEERING
3135 Euclid Avenue
Cleveland, OH 44115
P 216.391.3700 ext 3087
F 216.391.0108
E cbosch at karpinskieng.com
W www.karpinskieng.com
-----Original Message-----
From: Ömer Moltay [mailto:omoltay at mimtarch.com]
Sent: Monday, June 13, 2011 9:16 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Review Comment - Exhaust Fans
Dear All,
We have received the following from GBCI regarding the energy modelling
review:
"Table1.4.2 indicates that exhaust fan systems are reflected in the Proposed
model; however, the equipment capacities are inconsistent with the exhaust fan
systems (EF-1 through EF-9) as indicated in the mechanical schedules provided
for PI Form 4: Schedule and Overview Documents. In addition, the independent fan
systems of the HVAC systems in the actual design must be modeled identically
between the Proposed and Baseline models at actual equipment capacities (fan
volume and fan power) as required by Table G3.1.10 in the Proposed building
column, since the fan design air flow rates and fan power per Sections G3.1.2.8
and G3.1.2.9, respectively, only applies to system types 1 through 8 in Table
G3.1.1A.
Revise the
Proposed and Baseline models so all independentfan systems of the HVAC systems
are modeled identically between the Proposed and Baseline models. In addition,
separate the energy consumption and peak demand energy for independent#fans in
Table EAp2-4 and Table EAp2-5 of the prerequisite form. Further,provide revised
SV-A reports reflecting the changes"
Our proposed model has supply and exhaust fans (Supply: AHU, FCU -
Exhaust: AHU, independant exhaust fans). Our baseline model has supply and
relief fans (VAV System).
Please look at Section 6 of the attached Table 1.4.2. Are we expected to
additionally model exhaust fans in the baseline case? Do they mean exhaust fans
when they say "independent fan systems of the HVAC systems?".
Thanks for all replies,
Omer Moltay, LEED AP BD+C, BREEAM Assessor Mimta Ltd.
Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.mimtarch.com
www.mimtasolar.com
www.eko-yapi.net
Sürdürülebilir Binalar Blog
http://surdurulebilirbina.blogspot.com
Green Building in Turkey on LinkedIn
http://www.linkedin.com/groups?gid=2278249
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110618/2ec0bbb2/attachment-0002.htm>
More information about the Equest-users
mailing list