I've used the following approaches to model overheat gas radiant heating
systems.
Since doe-2 does not have models for heating that is predominantly radiant
in nature; the assumption I use for the heating models are that the
predominant gain mechanism is convection.
I assume the system is well modeled by using a heating coil in the space,
such as a baseboard system (which has no flow).
If the heater is constant output when on then you could use a reset
controlled baseboard with a flat output relation.
If they are space temperature controlled then you use thermostat control.
Both would be good models.
If control is variable based on people sense of comfort then you need a
relationship between space temperature and comfort and then alter the
thermostat schedule to match that relation.
Dennis
___________
Dennis Hunt
Mechanical Engineer
Summit Building Engineering
503-246-5241
dhunt at summitbe.com
http://www.summitbe.com
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Friday, May 25, 2012 8:30 AM
To: Pasgar, Arash; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Gas INFRA-RED Radiant
Hi Arash,
There are a couple right answers. Here's an approach I've used:
* System type UHT
* Zero out fan energy (0.00 kW/CFM), if there are no space
circulation fans tied to your IR heater operation
* eQuest doesn't simulate the skin-heating comfort effects of radiant
heat. If you run into unmet heating hours, you can justifiably lower
associated thermotat setpoints to account for this.
* DOE2 help files advise adjusting your HIR to 1.05 if products of
combustion are not being vented out of the space (industrial applications).
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasgar,
Arash
Sent: Friday, May 25, 2012 10:09 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Gas INFRA-RED Radiant
Hi all,
First of all sorry about the previous message.
I have a storage using gas infra-red radiant heaters. Is there accurate way
to model this.
Thank you in advance for your help.
Arash Pasgar
Mechanical Designer
Description: Description: Description: Description: Description:
Description: image001
v. 210.546.0200 | www.dbrinc.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120525/b75210f8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4870 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120525/b75210f8/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120525/b75210f8/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 984 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120525/b75210f8/attachment-0008.jpeg>
More information about the Equest-users
mailing list