[Equest-users] Indoor arena suggestions/tips
    Stormy L. Shanks 
    shankssl at kjww.com
       
    Thu Feb 28 14:59:53 PST 2013
    
    
  
Matt,
There is an addendum to 90.1 that adds heating-only systems 10 and 11. It's addendum dn. You might check it out, but I'm not sure that your space really fits into that addendum, and I don't think it helps you. When using that addendum, you model no cooling at all in either case. In reality, in the proposed building, you are getting some free cooling from natural ventilation.
I have an idea that's complicated but maybe other people have a simplified method that will accomplish something similar. If you were going to accurately demonstrate what you're saving over the baseline, you need to figure out how much energy your baseline system would use to do what the free cooling with natural ventilation is doing in the proposed model. Maybe you could figure out the space temperature you can achieve for each hour that you're using natural ventilation for free cooling. Then, you could set up a space setpoint schedule in your baseline that would match those temperatures. The mechanical cooling system in your baseline model would cool to those same temperatures. Does that sound crazy?
[cid:image001.png at 01CE0924.38506AB0]
Stormy L. Shanks, PE
Mechanical Engineer
2882 106th St, Des Moines, IA 50322
web<http://www.kjww.com/> | Facebook<http://www.facebook.com/kjwwengineering> | Twitter<http://twitter.com/kjww> | LinkedIn<http://www.linkedin.com/company/kjww-engineering-consultants>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Hein
Sent: Thursday, February 28, 2013 10:24 AM
To: RobertWichert; Email question to eQuest
Subject: Re: [Equest-users] Indoor arena suggestions/tips
Has anyone been able to capture savings from a natural ventilation design for LEED 2009 NC?  (I interpret that G3.1.1.b prevents this.)
Glancing over Appendix G I see something that doesn't seem very encouraging of 'green' design: (not to say that it discourages)
  *   G3.1.1.b says, "All conditioned spaces in the proposed design shall be simulated as being both heated and cooled even if no heating or cooling system is to be installed ..."
It seems like there should be some way to encourage natural ventilation design by accounting for the energy savings.
I suspect I'll approach this by setting a high Tstat value (100 F) and using the exact same cooling configuration for proposed and baseline so the savings are null. Well, maybe I can get some fan power savings.
- MRH
On 2/28/2013 8:33 AM, RobertWichert wrote:
I would certainly bring it up.  I would expect it to be more comfortable and with much lower fuel costs.  Even first cost could be lower, if you really plan to heat all that air, unless the insulation is very heavy, even on the roof.  I would think you could get away with minimal insulation on the roof if you used radiant.
Just my first thought though, I'm sure there is much more to consider.
Maybe you could keep us apprised of your progress...
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 2/27/2013 2:47 PM, Matt Hein wrote:
The preliminary design calls for forced-air with low winter setpoint of 60F and additional fans to de-stratify. Summer is Nat. ventilation with no cooling.
I plan on discussing radiant heat in our next conversation.
Thanks Robert,
- MRH
On 2/27/2013 4:02 PM, RobertWichert wrote:
Is radiant heating being discussed, Matt?
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 2/27/2013 1:27 PM, Matt Hein wrote:
Thanks David and Nick. Your advice is much appreciated.
- MRH
On 2/27/2013 1:58 PM, Nick Caton wrote:
No direct answers, but I would plan on a long discussion with the HVAC designers to arrive at a mutual understanding of the "conditioned volume" and loads incident on that volume to be addressed by the systems.  Approaching this as thermally-connected conditioned/unconditioned zones matching those design parameters makes sense procedurally from an eQuest standpoint.
Time permitting, running an early "test" model to ensure the results agree/ballpark with the designer's calculations would be a good idea as well to nail down the nuts & bolts of your modeling procedure before crunch time (Keeping good notes & written communication will also be helpful later for model documentation).
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matt Hein
Sent: Wednesday, February 27, 2013 10:32 AM
To: Email question to eQuest
Subject: [Equest-users] Indoor arena suggestions/tips
Hello all,
I'm working on an 150,000 sf indoor practice facility with 90 ft ceilings. Does anyone have any suggestions/tips/heads-up comments that would be useful in starting this model?
Specifically, I'm wondering if I'll run into issues related to stratification and need to create 'sub-zones' so eQuest better represents the proposed distribution system.
Thank you for your time and combined insight,
Matthew Hein, P.E.
BTU Engineering, Inc.
2021 25th Ave.
Brookings, SD  57006
Direct Phone: 605.695.8582
Toll Free: 888.288.2126
Fax: 888.288.2139
matthew.hein at btu-engineering.com<mailto:hein at BTU-Engineering.com>
www.BTU-Engineering.com<http://www.btu-engineering.com/>
  LinkedIn<http://www.linkedin.com/company/2439091?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>  |  Facebook<https://www.facebook.com/BTU.Engineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>  |  Google+ <https://plus.google.com/112692580402915348575/posts?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>  |  Twitter<https://twitter.com/BTUEngineering?utm_source=BTU+Engineering+Subscribers&utm_campaign=2c63bd2c50-Hello_from_BTU2_15_2013&utm_medium=email>  |  Subscribe to Email List<http://eepurl.com/uWeS9>
On 2/27/2013 10:50 AM, David Eldridge wrote:
eQUEST will assume a uniform temperature throughout the zone, so if the proposed HVAC system will allow stratification then you would need to do something like you are describing.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others.  Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130228/72f11007/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 9229 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130228/72f11007/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130228/72f11007/attachment-0002.jpg>
    
    
More information about the Equest-users
mailing list