[Equest-users] Section 179D Question
Paul Riemer
Paul.Riemer at dunhameng.com
Fri Apr 25 07:51:30 PDT 2014
The legislation clearly states ASHRAE 90.1-2001 as in effect on April 2, 2003 and lists which addenda that includes. The NREL published 'Guidelines' document says the same thing.
It combines tax law, accounting, building design, and energy modeling so yes there are lots of 'hiccups' out there.
Paul Riemer, PE, LEED AP BD+C
DUNHAM
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Jacobs
Sent: Friday, April 25, 2014 9:32 AM
To: Busby, Aaron; Tom Mickley; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Section 179D Question
I'm not aware of anything says we can or can't use addendum to Appendix G. It is certainly frustrating not having anywhere to take questions. The inability for modelers to seek clarifications means that the community is probably taking a lot of different approaches to the incentive.
On 4/25/2014 6:56 AM, Busby, Aaron wrote:
ASHRAE 90.1 has several addendums now that have added system types, just for warehouse type spaces where they are heated only. Look for Addenda DN, system types 10 and 11.
Aaron Busby, PE, LEED AP
Tel: 770.563.1522
Cell: 678.642.7549
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tom Mickley
Sent: Friday, April 25, 2014 8:38 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Section 179D Question
Has anyone run a baseline building for a retrofit building to qualify a business owner for the Section 179D tax deduction? It seems simple enough to model the existing building based on ASHRAE 90.1 standards. Has anyone found any potential "hiccups" along the way that has prevented the up to $1.80/sq tax deduction aside from the obvious of not meeting the energy upgrade percentage?
Here's my main concern. I have a cabinet manufacturer customer who has a 100,000sf metal building that is roughly 30% wood working or manufacturing, 65% warehouse storage and 5% office space. 95% of this facility is heated only. Do I have to include cooling in the baseline from ASHRAE 90.1 system 5 on appendix G, table G3.1.1.A? The only upgrades we are proposing are to take out the air rotation unit and radiant tube vacuum systems and a few other minor items.
Any advice would help. Thanks in advance.
Thanks,
Tom Mickley
Mechanical Engineer CEM
The K Company
Cell 330-760-3994
Office 330-773-5125
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140425/f66d7836/attachment-0002.htm>
More information about the Equest-users
mailing list