[EnergyPlus_Support] Modelling natural cross-ventilation using COMIS module



Hi,

I am evaluating using Energy Plus for modelling natural cross-ventilation 
for a hospital building. The basic strategy will be to cross ventilate the 
rooms, with air coming in from windows and exhausted through a stack in the 
roof. I am trying to do a very simple model of this using E+ and the COMIS 
module. I have modelled one zone with a window in the south face, and 
another zone on top of this to for the stack.

The problem is that i am not sure how to link the 2 zones together?

Also, i have seen that there is a passive stack component in COMIS 3.0, 
will this become available in the E+ COMIS module?

Kind regards

Colin Harris.


MODEL BELOW -

!-Generator IDFEditor 1.05

!-NOTE: All comments with '!-' are ignored by the IDFEditor and are 
generated automatically.
!-      Use '!' comments if they need to be retained when using the IDFEditor.


!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========

VERSION,
     1.0.1;                   !- Version Identifier


!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========

BUILDING,
     hospital,                !- Building Name
     0,                       !- North Axis {deg}
     Country,                 !- Terrain
     .04,                     !- Loads Convergence Tolerance Value {W}
     .4,                      !- Temperature Convergence Tolerance Value {C}
     MinimalShadowing;        !- Solar Distribution


!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP IN HOUR ===========

TIMESTEP IN HOUR,
      4;                      !- Time Step in Hour


!-   ===========  ALL OBJECTS IN CLASS: INSIDE CONVECTION ALGORITHM ===========

INSIDE CONVECTION ALGORITHM,
     Detailed;                !- InsideConvectionValue


!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE CONVECTION ALGORITHM 
===========

OUTSIDE CONVECTION ALGORITHM,
     Detailed;                !- OutsideConvectionValue


!-   ===========  ALL OBJECTS IN CLASS: SKY RADIANCE DISTRIBUTION ===========

SKY RADIANCE DISTRIBUTION,
      1;                      !- SkyRadianceValue


!-   ===========  ALL OBJECTS IN CLASS: SOLUTION ALGORITHM ===========

SOLUTION ALGORITHM,
     CTF;                     !- SolutionAlgo


!-   ===========  ALL OBJECTS IN CLASS: SHADOWING CALCULATIONS ===========

SHADOWING CALCULATIONS,
      20;                     !- Period_for_calculations


!-   ===========  ALL OBJECTS IN CLASS: AIRFLOW MODEL ===========

Airflow Model,
     COMIS;                   !- AirFlowModelValue


!-   ===========  ALL OBJECTS IN CLASS: ZONE VOLUME CAPACITANCE MULTIPLIER 
===========

ZONE VOLUME CAPACITANCE MULTIPLIER,
      1;                      !- Capacitance Multiplier


!-   ===========  ALL OBJECTS IN CLASS: RUN CONTROL ===========

RUN CONTROL,
     No,                      !- Do the zone sizing calculation
     No,                      !- Do the system sizing calculation
     No,                      !- Do the plant sizing calculation
     Yes,                     !- Do the design day simulations
     No;                      !- Do the weather file simulation


!-   ===========  ALL OBJECTS IN CLASS: DESIGNDAY ===========

DesignDay,
     SummerDayDUB-IRL,        !- DesignDayName
     26,                      !- Maximum Dry-Bulb Temperature {C}
     14,                      !- Daily Temperature Range {C}
     18,                      !- Wet-Bulb Temperature At MaxTemp {C}
     100000,                  !- Barometric Pressure {Pa}
     4,                       !- Wind Speed {m/s}
     180,                     !- Wind Direction {deg}
     1,                       !- Sky Clearness
     0,                       !- Rain Indicator
     0,                       !- Snow Indicator
     27,                      !- Day Of Month
     7,                       !- Month
     Friday,                  !- Day Type
     0;                       !- Daylight Saving Time Indicator


!-   ===========  ALL OBJECTS IN CLASS: GROUNDTEMPERATURES ===========

GroundTemperatures,
      5.5,                    !- January Ground Temperature {C}
     5.1,                     !- February Ground Temperature {C}
     6,                       !- March Ground Temperature {C}
     7.9,                     !- April Ground Temperature {C}
     10.5,                    !- May Ground Temperature {C}
     13,                      !- June Ground Temperature {C}
     14.6,                    !- July Ground Temperature {C}
     15.1,                    !- August Ground Temperature {C}
     14.2,                    !- September Ground Temperature {C}
     12.2,                    !- October Ground Temperature {C}
     9.7,                     !- November Ground Temperature {C}
     7.2;                     !- December Ground Temperature {C}


!-   ===========  ALL OBJECTS IN CLASS: GROUNDREFLECTANCES ===========

GroundReflectances,
      .2,                     !- January Ground Reflectance {dimensionless}
     .2,                      !- February Ground Reflectance {dimensionless}
     0.2,                     !- March Ground Reflectance {dimensionless}
     0.2,                     !- April Ground Reflectance {dimensionless}
     0.2,                     !- May Ground Reflectance {dimensionless}
     0.2,                     !- June Ground Reflectance {dimensionless}
     0.2,                     !- July Ground Reflectance {dimensionless}
     0.2,                     !- August Ground Reflectance {dimensionless}
     0.2,                     !- September Ground Reflectance {dimensionless}
     0.2,                     !- October Ground Reflectance {dimensionless}
     0.2,                     !- November Ground Reflectance {dimensionless}
     0.2;                     !- December Ground Reflectance {dimensionless}


!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:REGULAR ===========

MATERIAL:REGULAR,
     concreteWall,            !- Name
     MediumSmooth,            !- Roughness
     .3,                      !- Thickness {m}
     1.31,                    !- Conductivity {W/m-K}
     2240,                    !- Density {kg/m3}
     840,                     !- Specific Heat {J/kg-K}
     .9,                      !- Absorptance:Thermal
     .7,                      !- Absorptance:Solar
     .7;                      !- Absorptance:Visible


!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:WINDOWGLASS ===========

MATERIAL:WINDOWGLASS,
     windowGlass,             !- Name
     SpectralAverage,         !- Optical Data Type
     ,                        !- Name of Window Glass Spectral Data Set
     .01,                     !- Thickness {m}
     .9,                      !- Solar Transmittance at Normal Incidence
     .031,                    !- Solar Reflectance at Normal Incidence: 
Front Side
     .031,                    !- Solar Reflectance at Normal Incidence: 
Back Side
     .9,                      !- Visible Transmittance at Normal Incidence
     .05,                     !- Visible Reflectance at Normal Incidence: 
Front Side
     .05,                     !- Visible Reflectance at Normal Incidence: 
Back Side
     0,                       !- IR Transmittance at Normal Incidence
     .84,                     !- IR Hemispherical Emissivity: Front Side
     0.84,                    !- IR Hemispherical Emissivity: Back Side
     .9;                      !- Conductivity {W/m-K}


!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========

CONSTRUCTION,
     window,                  !- Name
     windowGlass;             !- Outside Layer

CONSTRUCTION,
     wall,                    !- Name
     concreteWall;            !- Outside Layer


!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========

ZONE,
     cube,                    !- Zone Name
     0,                       !- Relative North (to building) {deg}
     0,                       !- X Origin {m}
     0,                       !- Y Origin {m}
     0,                       !- Z Origin {m}
      1,                      !- Type
      1,                      !- Multiplier
      3,                      !- Ceiling Height {m}
      75;                     !- Volume {m3}

ZONE,
     exhaust,                 !- Zone Name
      0,                      !- Relative North (to building) {deg}
      2,                      !- X Origin {m}
      4,                      !- Y Origin {m}
      3,                      !- Z Origin {m}
      1,                      !- Type
     1,                       !- Multiplier
      1,                      !- Ceiling Height {m}
      1;                      !- Volume {m3}


!-   ===========  ALL OBJECTS IN CLASS: SURFACEGEOMETRY ===========

SurfaceGeometry,
     UpperLeftCorner,         !- SurfaceStartingPosition
     CounterClockWise,        !- VertexEntry
     relative;                !- SurfaceGeometryKey


!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER ===========

Surface:HeatTransfer,
     southWall,               !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     cube,                    !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     0,                       !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
     3,                       !- Vertex 1 Z-coordinate {m}
     0,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
     5,                       !- Vertex 3 X-coordinate {m}
     0,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
     5,                       !- Vertex 4 X-coordinate {m}
     0,                       !- Vertex 4 Y-coordinate {m}
     3;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     eastWall,                !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     cube,                    !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     5,                       !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
     3,                       !- Vertex 1 Z-coordinate {m}
     5,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
     5,                       !- Vertex 3 X-coordinate {m}
     5,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
     5,                       !- Vertex 4 X-coordinate {m}
     5,                       !- Vertex 4 Y-coordinate {m}
     3;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     roof,                    !- User Supplied Surface Name
     ROOF,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     cube,                    !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     0,                       !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     0,                       !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
     3,                       !- Vertex 1 Z-coordinate {m}
     5,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     3,                       !- Vertex 2 Z-coordinate {m}
     5,                       !- Vertex 3 X-coordinate {m}
     5,                       !- Vertex 3 Y-coordinate {m}
     3,                       !- Vertex 3 Z-coordinate {m}
     0,                       !- Vertex 4 X-coordinate {m}
     5,                       !- Vertex 4 Y-coordinate {m}
     3;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     floor,                   !- User Supplied Surface Name
     FLOOR,                   !- Surface Type
     wall,                    !- Construction Name of the Surface
     cube,                    !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     NoSun,                   !- Sun Exposure
     NoWind,                  !- Wind Exposure
     0,                       !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     5,                       !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
     0,                       !- Vertex 1 Z-coordinate {m}
     0,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
     0,                       !- Vertex 3 X-coordinate {m}
     5,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
     5,                       !- Vertex 4 X-coordinate {m}
     5,                       !- Vertex 4 Y-coordinate {m}
     0;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     northWall,               !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     cube,                    !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     5,                       !- Vertex 1 X-coordinate {m}
     5,                       !- Vertex 1 Y-coordinate {m}
     3,                       !- Vertex 1 Z-coordinate {m}
     5,                       !- Vertex 2 X-coordinate {m}
     5,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
     0,                       !- Vertex 3 X-coordinate {m}
     5,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
     0,                       !- Vertex 4 X-coordinate {m}
     5,                       !- Vertex 4 Y-coordinate {m}
     3;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     westWall,                !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     cube,                    !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     0,                       !- Vertex 1 X-coordinate {m}
     5,                       !- Vertex 1 Y-coordinate {m}
     3,                       !- Vertex 1 Z-coordinate {m}
     0,                       !- Vertex 2 X-coordinate {m}
     5,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
     0,                       !- Vertex 3 X-coordinate {m}
     0,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
     0,                       !- Vertex 4 X-coordinate {m}
     0,                       !- Vertex 4 Y-coordinate {m}
     3;                       !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     southExhaust,            !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     exhaust,                 !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
      .5,                     !- View Factor to Ground
      4,                      !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
      0,                      !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
      1,                      !- Vertex 1 Z-coordinate {m}
     0,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
      1,                      !- Vertex 3 X-coordinate {m}
     0,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
      1,                      !- Vertex 4 X-coordinate {m}
     0,                       !- Vertex 4 Y-coordinate {m}
      1;                      !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     eastExhaust,             !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     exhaust,                 !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
      1,                      !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
      1,                      !- Vertex 1 Z-coordinate {m}
      1,                      !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
      1,                      !- Vertex 3 X-coordinate {m}
      1,                      !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
      1,                      !- Vertex 4 X-coordinate {m}
      1,                      !- Vertex 4 Y-coordinate {m}
      1;                      !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     northExhaust,            !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     exhaust,                 !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
      1,                      !- Vertex 1 X-coordinate {m}
      1,                      !- Vertex 1 Y-coordinate {m}
      1,                      !- Vertex 1 Z-coordinate {m}
      1,                      !- Vertex 2 X-coordinate {m}
      1,                      !- Vertex 2 Y-coordinate {m}
      0,                      !- Vertex 2 Z-coordinate {m}
      0,                      !- Vertex 3 X-coordinate {m}
      1,                      !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
      0,                      !- Vertex 4 X-coordinate {m}
      1,                      !- Vertex 4 Y-coordinate {m}
      1;                      !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     westExhaust,             !- User Supplied Surface Name
     WALL,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     exhaust,                 !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     .5,                      !- View Factor to Ground
      4,                      !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
      0,                      !- Vertex 1 X-coordinate {m}
      1,                      !- Vertex 1 Y-coordinate {m}
      1,                      !- Vertex 1 Z-coordinate {m}
      0,                      !- Vertex 2 X-coordinate {m}
      1,                      !- Vertex 2 Y-coordinate {m}
      0,                      !- Vertex 2 Z-coordinate {m}
     0,                       !- Vertex 3 X-coordinate {m}
     0,                       !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
     0,                       !- Vertex 4 X-coordinate {m}
     0,                       !- Vertex 4 Y-coordinate {m}
      1;                      !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     roofExhaust,             !- User Supplied Surface Name
     ROOF,                    !- Surface Type
     wall,                    !- Construction Name of the Surface
     exhaust,                 !- InsideFaceEnvironment
     ExteriorEnvironment,     !- OutsideFaceEnvironment
     ,                        !- OutsideFaceEnvironment Object
     SunExposed,              !- Sun Exposure
     WindExposed,             !- Wind Exposure
     0,                       !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
      0,                      !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
      1,                      !- Vertex 1 Z-coordinate {m}
      1,                      !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
      1,                      !- Vertex 2 Z-coordinate {m}
      1,                      !- Vertex 3 X-coordinate {m}
      1,                      !- Vertex 3 Y-coordinate {m}
      1,                      !- Vertex 3 Z-coordinate {m}
     0,                       !- Vertex 4 X-coordinate {m}
      1,                      !- Vertex 4 Y-coordinate {m}
      1;                      !- Vertex 4 Z-coordinate {m}

Surface:HeatTransfer,
     floorExhaust,            !- User Supplied Surface Name
     FLOOR,                   !- Surface Type
     wall,                    !- Construction Name of the Surface
     exhaust,                 !- InsideFaceEnvironment
     OtherZoneSurface,        !- OutsideFaceEnvironment
     roof,                    !- OutsideFaceEnvironment Object
     NoSun,                   !- Sun Exposure
     NoWind,                  !- Wind Exposure
     0,                       !- View Factor to Ground
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
      1,                      !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
     0,                       !- Vertex 1 Z-coordinate {m}
     0,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     0,                       !- Vertex 2 Z-coordinate {m}
     0,                       !- Vertex 3 X-coordinate {m}
      1,                      !- Vertex 3 Y-coordinate {m}
     0,                       !- Vertex 3 Z-coordinate {m}
      1,                      !- Vertex 4 X-coordinate {m}
      1,                      !- Vertex 4 Y-coordinate {m}
     0;                       !- Vertex 4 Z-coordinate {m}


!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER:SUB ===========

Surface:HeatTransfer:Sub,
     windowSouth,             !- User Supplied Surface Name
     WINDOW,                  !- Surface Type
     window,                  !- Construction Name of the Surface
     southWall,               !- Base Surface Name
     ,                        !- OutsideFaceEnvironment Object
     .5,                      !- View Factor to Ground
     ,                        !- Name of shading control
     ,                        !- WindowFrameAndDivider Name
     1,                       !- Multiplier
     4,                       !- Number of Surface Vertice Groups -- Number 
of (X,Y,Z) groups in this surface
     2,                       !- Vertex 1 X-coordinate {m}
     0,                       !- Vertex 1 Y-coordinate {m}
     2,                       !- Vertex 1 Z-coordinate {m}
     2,                       !- Vertex 2 X-coordinate {m}
     0,                       !- Vertex 2 Y-coordinate {m}
     1,                       !- Vertex 2 Z-coordinate {m}
     3,                       !- Vertex 3 X-coordinate {m}
     0,                       !- Vertex 3 Y-coordinate {m}
     1,                       !- Vertex 3 Z-coordinate {m}
     3,                       !- Vertex 4 X-coordinate {m}
     0,                       !- Vertex 4 Y-coordinate {m}
     2;                       !- Vertex 4 Z-coordinate {m}


!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPE ===========

ScheduleType,
     Any Number,              !- ScheduleType Name
     ,                        !- range
     CONTINUOUS;              !- Numeric Type


!-   ===========  ALL OBJECTS IN CLASS: DAYSCHEDULE ===========

DAYSCHEDULE,
     infiltrationSchedule,    !- Name
     Any Number,              !- ScheduleType
     .5,                      !- Hour 1
     .5,                      !- Hour 2
     .5,                      !- Hour 3
     .5,                      !- Hour 4
     .5,                      !- Hour 5
     .5,                      !- Hour 6
     .5,                      !- Hour 7
     1,                       !- Hour 8
     1,                       !- Hour 9
     1,                       !- Hour 10
     1,                       !- Hour 11
     1,                       !- Hour 12
     1,                       !- Hour 13
     1,                       !- Hour 14
     1,                       !- Hour 15
     1,                       !- Hour 16
     1,                       !- Hour 17
     1,                       !- Hour 18
     1,                       !- Hour 19
     .5,                      !- Hour 20
     .5,                      !- Hour 21
     .5,                      !- Hour 22
     .5,                      !- Hour 23
     .5;                      !- Hour 24

DAYSCHEDULE,
     ventTempSch,             !- Name
     Any Number,              !- ScheduleType
     20,                      !- Hour 1
     20,                      !- Hour 2
     20,                      !- Hour 3
     20,                      !- Hour 4
     20,                      !- Hour 5
     20,                      !- Hour 6
     20,                      !- Hour 7
     20,                      !- Hour 8
     20,                      !- Hour 9
     20,                      !- Hour 10
     20,                      !- Hour 11
     20,                      !- Hour 12
     20,                      !- Hour 13
     20,                      !- Hour 14
     20,                      !- Hour 15
     20,                      !- Hour 16
     20,                      !- Hour 17
     20,                      !- Hour 18
     20,                      !- Hour 19
     20,                      !- Hour 20
     20,                      !- Hour 21
     20,                      !- Hour 22
     20,                      !- Hour 23
     20;                      !- Hour 24

DAYSCHEDULE,
     ventTempSch23,           !- Name
     Any Number,              !- ScheduleType
     23,                      !- Hour 1
     23,                      !- Hour 2
     23,                      !- Hour 3
     23,                      !- Hour 4
     23,                      !- Hour 5
     23,                      !- Hour 6
     23,                      !- Hour 7
     23,                      !- Hour 8
     23,                      !- Hour 9
     23,                      !- Hour 10
     23,                      !- Hour 11
     23,                      !- Hour 12
     23,                      !- Hour 13
     23,                      !- Hour 14
     23,                      !- Hour 15
     23,                      !- Hour 16
     23,                      !- Hour 17
     23,                      !- Hour 18
     23,                      !- Hour 19
     23,                      !- Hour 20
     23,                      !- Hour 21
     23,                      !- Hour 22
     23,                      !- Hour 23
     23;                      !- Hour 24


!-   ===========  ALL OBJECTS IN CLASS: WEEKSCHEDULE ===========

WEEKSCHEDULE,
     infiltrationWeek,        !- Name
     infiltrationSchedule,    !- Sunday DAYSCHEDULE Name
     infiltrationSchedule,    !- Monday DAYSCHEDULE Name
     infiltrationSchedule,    !- Tuesday DAYSCHEDULE Name
     infiltrationSchedule,    !- Wednesday DAYSCHEDULE Name
     infiltrationSchedule,    !- Thursday DAYSCHEDULE Name
     infiltrationSchedule,    !- Friday DAYSCHEDULE Name
     infiltrationSchedule,    !- Saturday DAYSCHEDULE Name
     infiltrationSchedule,    !- Holiday DAYSCHEDULE Name
     infiltrationSchedule,    !- SummerDesignDay DAYSCHEDULE Name
     infiltrationSchedule,    !- WinterDesignDay DAYSCHEDULE Name
     infiltrationSchedule,    !- CustomDay1 DAYSCHEDULE Name
     infiltrationSchedule;    !- CustomDay2 DAYSCHEDULE Name

WEEKSCHEDULE,
     ventTempWeek,            !- Name
     ventTempSch,             !- Sunday DAYSCHEDULE Name
     ventTempSch,             !- Monday DAYSCHEDULE Name
     ventTempSch,             !- Tuesday DAYSCHEDULE Name
     ventTempSch,             !- Wednesday DAYSCHEDULE Name
     ventTempSch,             !- Thursday DAYSCHEDULE Name
     ventTempSch,             !- Friday DAYSCHEDULE Name
     ventTempSch,             !- Saturday DAYSCHEDULE Name
     ventTempSch,             !- Holiday DAYSCHEDULE Name
     ventTempSch,             !- SummerDesignDay DAYSCHEDULE Name
     ventTempSch,             !- WinterDesignDay DAYSCHEDULE Name
     ventTempSch,             !- CustomDay1 DAYSCHEDULE Name
     ventTempSch;             !- CustomDay2 DAYSCHEDULE Name


!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE ===========

SCHEDULE,
     AirflowSchedule,         !- Name
     Any Number,              !- ScheduleType
     infiltrationWeek,        !- Name of WEEKSCHEDULE 1
     1,                       !- Start Month 1
     1,                       !- Start Day 1
     12,                      !- End Month 1
     31;                      !- End Day 1

SCHEDULE,
     VentTempSchedule,        !- Name
     Any Number,              !- ScheduleType
     ventTempWeek,            !- Name of WEEKSCHEDULE 1
     1,                       !- Start Month 1
     1,                       !- Start Day 1
     12,                      !- End Month 1
     31;                      !- End Day 1


!-   ===========  ALL OBJECTS IN CLASS: COMIS SIMULATION ===========

COMIS SIMULATION,
     VENT,                    !- Ventilation simulation control
     NO POL,                  !- Pollution simulation control
     NO CONC,                 !- Concentration simulation control
     1,                       !- Under relaxation factor {dimensionless}
     .000001,                 !- Absolute flow tolerance {kg/s}
     .00001,                  !- Relative flow tolerance {dimensionless}
     .0001,                   !- Error estimation for total flow per zone 
{kg/s}
     1,                       !- Start number of iterations
     .0001,                   !- Limit for laminar flow approximation {Pa}
     2,                       !- Flag for using old pressures
     1,                       !- Flag for pressure initiation
     50000,                   !- Max number of iterations
     10,                      !- Reference height for recorded wind data {m}
     .14,                     !- Wind velocity profile exponent {dimensionless}
     simple CP data;          !- CP Set Name


!-   ===========  ALL OBJECTS IN CLASS: COMIS ZONE DATA ===========

COMIS Zone Data,
     cube,                    !- Zone Name (points to Zone)
     VentTempSchedule,        !- Vent Temperature Schedule
     TEMPERATURE;             !- Ventilation Mode

COMIS Zone Data,
     exhaust,                 !- Zone Name (points to Zone)
     VentTempSchedule,        !- Vent Temperature Schedule
     TEMPERATURE;             !- Ventilation Mode


!-   ===========  ALL OBJECTS IN CLASS: COMIS SURFACE DATA ===========

COMIS Surface Data,
     windowSouth,             !- Surface Name (points to surface)
     window,                  !- Air Flow Crack or Opening Type
     1,                       !- External Node
      1;                      !- Crack Actual Value or Window Open Factor 
for Ventilation {dimensionless}

COMIS Surface Data,
     southWall,               !- Surface Name (points to surface)
     CracksWall,              !- Air Flow Crack or Opening Type
     1,                       !- External Node
     1;                       !- Crack Actual Value or Window Open Factor 
for Ventilation {dimensionless}

COMIS Surface Data,
     eastWall,                !- Surface Name (points to surface)
     CracksWall,              !- Air Flow Crack or Opening Type
     4,                       !- External Node
     1;                       !- Crack Actual Value or Window Open Factor 
for Ventilation {dimensionless}

COMIS Surface Data,
     northWall,               !- Surface Name (points to surface)
     CracksWall,              !- Air Flow Crack or Opening Type
     2,                       !- External Node
     1;                       !- Crack Actual Value or Window Open Factor 
for Ventilation {dimensionless}

COMIS Surface Data,
     westWall,                !- Surface Name (points to surface)
     CracksWall,              !- Air Flow Crack or Opening Type
     3,                       !- External Node
     1;                       !- Crack Actual Value or Window Open Factor 
for Ventilation {dimensionless}

COMIS Surface Data,
     northExhaust,            !- Surface Name (points to surface)
     window,                  !- Air Flow Crack or Opening Type
      5,                      !- External Node
      1;                      !- Crack Actual Value or Window Open Factor 
for Ventilation {dimensionless}


!-   ===========  ALL OBJECTS IN CLASS: COMIS SITE WIND CONDITIONS ===========

COMIS SITE WIND CONDITIONS,
      0,                      !- Wind direction angle {deg}
     5,                       !- Plan area density {dimensionless}
     .12,                     !- Wind velocity profile exponent {dimensionless}
     0;                       !- Surrounding building height {m}

COMIS SITE WIND CONDITIONS,
     90,                      !- Wind direction angle {deg}
     5,                       !- Plan area density {dimensionless}
     .12,                     !- Wind velocity profile exponent {dimensionless}
     0;                       !- Surrounding building height {m}

COMIS SITE WIND CONDITIONS,
     180,                     !- Wind direction angle {deg}
     5,                       !- Plan area density {dimensionless}
     .12,                     !- Wind velocity profile exponent {dimensionless}
     0;                       !- Surrounding building height {m}

COMIS SITE WIND CONDITIONS,
     270,                     !- Wind direction angle {deg}
     5,                       !- Plan area density {dimensionless}
     .12,                     !- Wind velocity profile exponent {dimensionless}
     0;                       !- Surrounding building height {m}


!-   ===========  ALL OBJECTS IN CLASS: COMIS EXTERNAL NODE ===========

COMIS EXTERNAL NODE,
     southFacade,             !- Facade element name
     0;                       !- Outside concentration factor {dimensionless}

COMIS EXTERNAL NODE,
     northFacade,             !- Facade element name
     0;                       !- Outside concentration factor {dimensionless}

COMIS EXTERNAL NODE,
     westFacade,              !- Facade element name
      0;                      !- Outside concentration factor {dimensionless}

COMIS EXTERNAL NODE,
     eastFacade,              !- Facade element name
     0;                       !- Outside concentration factor {dimensionless}

COMIS EXTERNAL NODE,
     northExhaustFacade,      !- Facade element name
      0;                      !- Outside concentration factor {dimensionless}


!-   ===========  ALL OBJECTS IN CLASS: COMIS STANDARD CONDITIONS FOR CRACK 
DATA ===========

COMIS STANDARD CONDITIONS FOR CRACK DATA,
      20,                     !- Standard temperature for crack data {C}
     101.32,                  !- Standard barometric pressure for crack 
data {kPa}
     5;                       !- Standard humidity for crack data {g/kg}


!-   ===========  ALL OBJECTS IN CLASS: COMIS AIR FLOW:CRACK ===========

COMIS AIR FLOW:Crack,
     CracksWall,              !- User Supplied airflow data name
     .001,                    !- Air mass flow coefficient {kg/s @ 1Pa}
     .667,                    !- Air flow exponent {dimensionless}
     1,                       !- Crack length {m}
     0,                       !- Pollution filter 1 {dimensionless}
     0,                       !- Pollution filter 2 {dimensionless}
     0;                       !- Pollution filter 3 {dimensionless}


!-   ===========  ALL OBJECTS IN CLASS: COMIS AIR FLOW:OPENING ===========

COMIS AIR FLOW:Opening,
     window,                  !- User Supplied airflow data name
     .001,                    !- Flow coefficient for closed window {kg/s @ 
1Pa per m crack length}
     .667,                    !- Flow exponent for closed window 
{dimensionless}
      1,                      !- Type of large vertical opening (LVO)
     0,                       !- Extra crack length for LVO type 1 with 
multiple parts or Height of pivoting axis for LVO type 2 {m}
     2,                       !- Number of Opening Factors (Max 4)
     0,                       !- Opening factor 1 {dimensionless}
     .6,                      !- Discharge coefficient 1 {dimensionless}
     0,                       !- Width factor for LVO type 1 {dimensionless}
     1,                       !- Height factor for LVO type 1 {dimensionless}
     0,                       !- Start height factor for LVO type 1 
{dimensionless}
     1,                       !- Opening factor 2 {dimensionless}
     .6,                      !- Discharge coefficient 2 {dimensionless}
     1,                       !- Width factor for LVO type 2 {dimensionless}
     1,                       !- Height factor for LVO type 2 {dimensionless}
     0,                       !- Start height factor for LVO type 2 
{dimensionless}
     ,                        !- Opening factor 3 {dimensionless}
     ,                        !- Discharge coefficient 3 {dimensionless}
     ,                        !- Width factor for LVO type 3 {dimensionless}
     ,                        !- Height factor for LVO type 3 {dimensionless}
     ,                        !- Start height factor for LVO type 3 
{dimensionless}
     ,                        !- Opening factor 4 {dimensionless}
     ,                        !- Discharge coefficient 4 {dimensionless}
     ,                        !- Width factor for LVO type 4 {dimensionless}
     ,                        !- Height factor for LVO type 4 {dimensionless}
     ,                        !- Start height factor for LVO type 4 
{dimensionless}
     0,                       !- Pollution filter 1 {dimensionless}
     0,                       !- Pollution filter 2 {dimensionless}
     0,                       !- Pollution filter 3 {dimensionless}
     0,                       !- Pollution filter 4 {dimensionless}
     0;                       !- Pollution filter 5 {dimensionless}


!-   ===========  ALL OBJECTS IN CLASS: COMIS CP ARRAY ===========

COMIS CP ARRAY,
     simple CP data,          !- CP Set Name
     10,                      !- Reference height for CP data {m}
     0,                       !- Wind direction 1 {deg}
     90,                      !- Wind direction 2 {deg}
     180,                     !- Wind direction 3 {deg}
     270;                     !- Wind direction 4 {deg}


!-   ===========  ALL OBJECTS IN CLASS: COMIS CP VALUES ===========

COMIS CP VALUES,
     simple CP data,          !- CP Set Name
     southFacade,             !- Facade element name
     -.5,                     !- Cp value 1 {dimensionless}
     -.5,                     !- Cp value 2 {dimensionless}
     .5,                      !- Cp value 3 {dimensionless}
     -.5;                     !- Cp value 4 {dimensionless}

COMIS CP VALUES,
     simple CP data,          !- CP Set Name
     northFacade,             !- Facade element name
     .5,                      !- Cp value 1 {dimensionless}
     -.5,                     !- Cp value 2 {dimensionless}
     -.5,                     !- Cp value 3 {dimensionless}
     -.5;                     !- Cp value 4 {dimensionless}

COMIS CP VALUES,
     simple CP data,          !- CP Set Name
     westFacade,              !- Facade element name
     -.5,                     !- Cp value 1 {dimensionless}
     -.5,                     !- Cp value 2 {dimensionless}
     -.5,                     !- Cp value 3 {dimensionless}
     .5;                      !- Cp value 4 {dimensionless}

COMIS CP VALUES,
     simple CP data,          !- CP Set Name
     eastFacade,              !- Facade element name
     -.5,                     !- Cp value 1 {dimensionless}
     .5,                      !- Cp value 2 {dimensionless}
     -.5,                     !- Cp value 3 {dimensionless}
     -.5;                     !- Cp value 4 {dimensionless}

COMIS CP VALUES,
     simple CP data,          !- CP Set Name
     northExhaustFacade,      !- Facade element name
     .5,                      !- Cp value 1 {dimensionless}
     -.5,                     !- Cp value 2 {dimensionless}
     -.5,                     !- Cp value 3 {dimensionless}
     -.5;                     !- Cp value 4 {dimensionless}


!-   ===========  ALL OBJECTS IN CLASS: REPORT VARIABLE ===========

Report Variable,
     ,                        !- Key_Value
     Outdoor Dry Bulb,        !- Variable_Name
     hourly;                  !- Reporting_Frequency

Report Variable,
     ,                        !- Key_Value
     Mean Air Temperature,    !- Variable_Name
     hourly;                  !- Reporting_Frequency

Report Variable,
     ,                        !- Key_Value
     Infiltration-Heat Loss,  !- Variable_Name
     hourly;                  !- Reporting_Frequency

Report Variable,
     ,                        !- Key_Value
     Infiltration-Volume,     !- Variable_Name
     hourly;                  !- Reporting_Frequency

Report Variable,
     ,                        !- Key_Value
     Infiltration-Heat Gain,  !- Variable_Name
     hourly;                  !- Reporting_Frequency


!-   ===========  ALL OBJECTS IN CLASS: REPORT ===========

Report,
     Surfaces,                !- Type_of_Report
     DXF;                     !- Name_of_Report

Report,
     Variable Dictionary;     !- Type_of_Report

Report,
     Surfaces,                !- Type_of_Report
     DETAILS;                 !- Name_of_Report




------------------------ Yahoo! Groups Sponsor ---------------------~-->
Will You Find True Love?
Will You Meet the One?
Free Love Reading by phone!
http://us.click.yahoo.com/Deo18C/zDLEAA/Ey.GAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/