Shefali:

The airflow modeling can be done using the COMIS airflow model.  
Given a vertical window, COMIS can model the airflow impact of 
opening a horizontally pivoted window to a certain angle.

I do not see a way to model the solar gains of the open window.  If I 
understand your intent, when such a window is open, there are times 
of the day when some of the sunlight can directly enter the space 
without going through glass, some of the sunlight will pass through 
the tilted glass and then enter the space directly, and some will 
pass through the tilted glass and then enter the space by passing 
through the window below it which may also be open or may be vertical.

If you were to specify the window coordinates in it's tilted 
position, the shadowing and interior solar distribution routines will 
have difficulty with the protruding glass.

Mike 


On 17 Jul 2002, at 18:54, Shefali Rajendra Modi wrote:

> I am trying to study the impact on heat gain by different types of airflow
> through  the double skin envelope. So I guess I am modeing for both, solar
> and ventilation.
> 
> Can that be done in energy plus?
> thanks
> Shefali
> 
> --------------------------------------------------------
> Shefali Modi
> M.Sc. Architecture, Environmental Technology
> Art and Architecture Building 2094
> 
> On Wed, 17 Jul 2002, Michael J. Witte wrote:
> 
> > Shefali:
> >
> > What effect are you trying to model?  Solar, or ventilation?
> >
> > "View factor to ground" changes the balance of sky diffuse vs. ground-
> > reflected diffuse solar which hits the window, and this is a fixed
> > value for the entire simulation.
> >
> > Mike Witte
> >
> > On 16 Jul 2002, at 14:55, Shefali Rajendra Modi wrote:
> >
> > >
> > > Hi,
> > >
> > > While modeling a simple room, I would like to use different angles of
> > > window opening. Assuming that the windows open along the horizontal axis,
> > > would the "view factor to the ground" be the correct place to specify this
> > > angle of window opening. If not can you guide me on how to specify opening
> > > angles.
> > >
> > > thank you
> > > Shefali
> > >
> > > --------------------------------------------------------
> > > Shefali Modi
> > > M.Sc. Architecture, Environmental Technology
> > > Art and Architecture Building 2094
> > >
> > >
> > >
> > >
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > >
> > >
> > >
> > >
> > >
> > > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> > >
> > >
> > >
> >
> >
> >
> > ========================================================
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> >
> >
> 
> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> 
> 
> 
>  
> 
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/ 
> 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Will You Find True Love?
Will You Meet the One?
Free Love Reading by phone!
http://us.click.yahoo.com/ps3dMC/R_ZEAA/Ey.GAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/