At 07:44 AM 7/22/02, rmp4aup6 wrote:
>First is about the object of Surface:Surface:Detached. In my thinking,
>I supposed that it will influence the temperature of  wall (outside
>and therefore inside), am I right?
>But after I input all the parameter in the object including
>User Supplied Surface Name, TransSchedShadowSurf, Number of Surface
>Vertice Groups and coordinate. The simulation result was the same with
>the one before that I didn't input the parameters in the
>Surface:Detached object. Is there something wrong?

A better indication of whether you have the detached shading parameters 
correct is to look at the sunlit area or sunlit fraction of the shaded 
surface.  It should change when the surface is shaded.  Yes, the exterior 
surface temperature should change as well -- but there are other influences 
on the inside surface temperature.

For V1.0.1, the detached surface shades from "behind" itself.  Therefore, a 
south facing wall needs a "north facing" detached shade to make an 
effect.  This limitation goes away in V1.0.2 due to the addition of 
bi-directional shading devices and makes it less important to get the 
orientation of the shading devices correct.

Linda


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Free $5 Love Reading
Risk Free!
http://us.click.yahoo.com/wlyPtD/PfREAA/Ey.GAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/