The design day data in the weather files are taken from the ASHRAE
Hanbook of Fundamentals and include data for several different design
points, Heating (99.6% and 99%), Cooling Dry Bulb (0.4%, 1% and
2%), Wet Bulb (0.4%, 1%, and 2%), and Dew Point (0.4%, 1%, and 2%).
From this information, you can then create design day objects as
desired. As Linda mentioned, the creation of design day objects will
be automated in the v1.0.3 release.
For each design day type, the user must decide which percentile to
design to. This may be dictated by local codes.
For heating, most users typically use a single design day, typcially
with no range in temperature (the high equals the low for the day),
and with no sun (clearness=0). This is a conservative assumption.
For cooling, one dry bulb design day is necessary, with sun
(clearness = approximately 1.0), and with a range in temperature,
specified by the daily range value in the design data.
In most climates, except very dry climates, it is also important to
run a dew point day. In applications with significant outside air
requirements, the peak total (sensible+latent) cooling load on the
dew point day can exceed the peak load on the dry bulb cooling day.
For cetain applications, it may also be necessary to run a wet bulb
design day as well.
Mike
On 3 Oct 2002, at 6:26, Linda Lawrie wrote:
> At 06:39 AM 10/2/2002, Alexander wrote:
> >Dear Sir/Madam
> >The weatherfiles include design day and groundtemperature data. How
> >do these correspond to the IDF objects DesignDay and
> >GroundTemperatures?
>
> (Ground temperature question answered in a separate email)
>
> The design day information will be able to be transformed into
> DesignDay objects in release V1.0.3. The entire set of "design
> conditions" will be available (along with location objects) as well as
> each individual weather file that includes design information can be
> generate this information separately.
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Sell a Home for Top $
http://us.click.yahoo.com/RrPZMC/jTmEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/