Sorry, the list of valid window layers hasn't kept up with some of
the new object types. Valid window layers are:
MATERIAL:WINDOWGLASS
MATERIAL:WINDOWGLASS:AltInput
MATERIAL:WINDOWGAS
MATERIAL:WINDOWGASMIXTURE
MATERIAL:WINDOWSHADE
MATERIAL:WINDOWBLIND
Page 70 of the Input/Output reference lists the following rules for
window constructions:
"The gap between the inside glass layer (layer #3) and the shading
layer is not entered. A maximum of four glass layers and one shading
layer is allowed. If there is a shading layer, it must be the first
or last layer (no between-pane shading devices!). A gas layer must
always separate adjacent glass layers in a multi-pane glazing."
Also, it would not be valid to put two gas layers adjacent to each
other, because the resistance of a gas layer is dependent upon the
thickness of the gap. The resistance of two 1cm gaps is not
necessarily the same as the resistance of a 2cm gap.
Mike
On 25 Oct 2002, at 7:19, TangoJim wrote:
> For constructing a glazing assembly, the documentation
> indicates that the following E+ commands can be used
> for defining the layers: Material:WindowGlass,
> Material:WindowGas and Material:WindowShade.
>
> Questions
>
> 1) Can Material:GasMixture be used for a layer?
>
> 2) Can Material:WindowGlassAlt be used for a layer?
>
> 3) Are there any rules like: two solid glazing
> materials cannot be next to each other, two gas
> materials cannot be next to each other, and Window
> Shading materials must be either on the outside layer
> or the inside layer?
>
> __________________________________________________
> Do you Yahoo!?
> Y! Web Hosting - Let the expert host your web site
> http://webhosting.yahoo.com/
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> 4 DVDs Free +s&p Join Now
> http://us.click.yahoo.com/pt6YBB/NXiEAA/jd3IAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/