[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Capabilities and modules of EnergyPlus
At 01:48 PM 1/7/2003, lengjing lengjing wrote:
>I wonder if there is a complete list
>of models (or modules) of EnergyPlus for different
>types of equipment related to building simulation.
Maybe not a complete list. Several of the papers that can be viewed at the
main web site (www.energyplus.gov) have tables comparing the 3 programs
(EnergyPlus, BLAST, and DOE-2) but I don't think we've compiled a complete
list. Perhaps if you ask in the "area" you are looking for, we can give
some specifics.
>Does EnergyPlus have all the modeling capabilities of
>and inherit all the equipment models from DOE-2 and
>BLAST?
That is our goal but not quite achieved yet. On the other hand, in some
areas EnergyPlus goes far beyond what either DOE-2 or BLAST could do.
> For example, I heard that DOE-2 has a
>refrigerated case equipment model that can be used to
>calculate the case load as well as its contribution to
>the space AC load for supermarket simulation. Does
>EnergyPlus have this?
I believe this is on our development list but not fully incorporated yet.
>Is there any validation of E+ for humidity control and
>simulation with the predictor-corrector algorithm?
Are you familiar with the testing that EnergyPlus has undergone? Specifics
on the test comparisons to analytical tests and with other programs are
again available from the main web site.
>How's thermal mass/furniture modeled in E+?
Thermal mass is modeled through the conduction transfer function method
that we use and then interacts with the heat balance of the zones in the
building. This is documented in various places. Furniture, if needed for
the model, would be included as an "internal mass" object.
>Is it
>possible to obtain the transient thermal responses of
>the indoor air and building structure at startup and
>shutdown?
Yes, though not exactly sure what you are requesting.
> Is 15 minutes still the minimum time step
>that can be used for predictions of temperature,
>humidity and building load?
Still? 15 minutes has never been the minimum time step for simulation
though it is the recommended time step for non-HVAC models. Most of our
HVAC models use 10 minute time steps. Note that we also have two FAQ
questions dealing with Time Step:
Q: [Time Step] What is the difference between the TimeStep indicated in the
TimeStep in Hour object and the "variable" timestep indicated in the HVAC
simulation (ref. Engineering Documentation)?
A: The TimeStep In Hour object specifies the "basic" time step for the
simulation. This is used in the Heat Balance calculation as the driving
time step. When the HVAC portion of the simulation begins it's solution
for the current time step, it uses the basic time step as its maximum but
then can reduce the time step, as necessary, to reach the solution.
The technical details of the approach are explained in the
<EngineeringDoc.htm>Engineering Documentation, under "Integrated Solution
Manager".
Users can see the effect/actual HVAC time step used if they select the
"detailed" option on an HVAC report variable (e.g. Zone/Sys Air Temp). To
contrast, the "Zone" variables will only be reported on the Heat Balance
time step (e.g. Mean Air Temperature).
Q: [Time Step] Time steps recommended in E+ is 4 for non-HVAC and 6 for
HVAC calculations. Does it mean using time step of 1 will cause E+ to
diverge or sacrifice the accuracy?
A: Actually, 4 or 6 Time steps per hour are necessary for the HVAC
calculations. The heat balance simulation will give reasonable results at
1, 4, or 6 Time steps per hour.
Note that the Time Step value must be evenly divisible into 60 -- therefore
is limited to:
1,2,3,4,5,6,10,12,15,30,60
>Thank you very much in advance for your help.
You're welcome. I think many of your questions may be answered in our
documentation which comes with the program -- again available for download
(free of charge) from the main web site.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Flexible Keyboard is the ideal accessory for PDA users that are on the move.
http://us.click.yahoo.com/dCBVZC/WnCFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/