Re: [EnergyPlus_Support] Constant Air Flow into rooms
Franz:
Describe an air loop with a supply fan and specify the supply air
volume flow rate for the fan. Use the constant volume CVBBrh example
as a guide and delete the coils.
Mike
On 29 Jan 2003, at 11:53, Franz Muller wrote:
> Dear E+ user,
>
> i want to get fresh (outside) air without any warming up into my
> rooms. I want to bring this fresh air into the rooms using a fan and a
> splitter and "direct air"- the exhaust flow of the rooms shall go via
> a mixer and a second fan outside. I don't want to use any further
> coils or AC-systems. The module shall keep quite simple.
>
> How can I tell the built system the air mass flow? I just want to say
> it shall be constant for all the time (so it also shall be on during
> night and weekends). The flow shall be 2 kg/s.
>
> I hope that anybody could help me. I looked up the examples but they
> don't fit.
>
> Kind regards
>
> Franz
>
>
> --
> +++ GMX - Mail, Messaging & more http://www.gmx.net +++
> NEU: Mit GMX ins Internet. Rund um die Uhr für 1 ct/ Min. surfen!
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/