Andy:
I was out of the office last week. It will probably be tomorrow
before I can look at your file. If you bring yourself to look at it
again (:-) the problem is probably in the return air path. An
incorrect node name can leave the zones disconnected from the air
loop so that the air loop does not know it needs to operate.
Mike
On 31 Jan 2003, at 9:59, Phelps, Andrew T ERDC-CERL-IL Contractor wrote:
> So here is the story:
> I cut and pasted the VAVreheat model into my model. I made the
> modification to make it fit my building, and repeated this 4 more
> times (it seems that EnergyPlus will handle only 1 supply plenum, and
> I had modeled 5 before I found this fact out). Finally after fixing
> the syntax errors so that the simulation would run, I set the computer
> loose to do its work. --side note-- the computer I was given here at
> work is extremely old (a 486), it took 4 hours for the processor to
> complete the simulation. -- So, I open the csv file this morning, and
> it seems that the HVAC was never turned on. I am tired of looking at
> the idf file, and feel that having someone else look at it would be
> helpful. So, if you have any comments or suggestions, please pass
> them on.
>
> Thank you very much.
>
> Andy
>
>
> [Non-text portions of this message have been removed]
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/