Re: [EnergyPlus_Support] Node Types Undefined



Hello,
This actually looks like you mis-named the chiller component.  The object 
name for that chiller is:
     CHILLER:CONST COP

I think you are missing the T from CONST.  Change that and see if the error 
message changes.

Thanks Richard Liesen

At 04:49 AM 7/1/2003, Santiago Torres wrote:
>Hello,
>
>I am having problems with a simple model I adapted
>from the DualDuctConstVolDumper example. The
>simulation runs fine but I receive several Warnings
>like this:
>
>** Warning ** Potential Node Connection Error for
>object CHILLER:CONS COP, name=HP2
>**   ~~~   **   Node Types are still UNDEFINED -- See
>Branch/Node Details file for further information
>**   ~~~   **   Inlet Node : COND_HP2_IN
>**   ~~~   **   Outlet Node: COND_HP2_OUT
>
>and in the .bnd file:
>
>Component Set,22,BRANCH,COND_HP2_BR,CHILLER:CONS
>COP,HP2,COND_HP2_IN,COND_HP2_OUT,UNDEFINED
>
>Could anyone please explain me what am I doing wrong?
>I checked with the exaple file and everything seems
>the same, except that I changed the node names (the
>exaple file doesn`t produce these warnings). Must the
>node names follow some kind of syntax?
>Thank you in advance,
>
>Santiago.
>
>
>_________________________________________________________
>Do You Yahoo!?
>Información de Estados Unidos y América Latina, en Yahoo! Noticias.
>Visítanos en http://noticias.espanol.yahoo.com
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/