Re: [EnergyPlus_Support] Node Types Undefined
Thank you very much for your reply. I checked again
and this was in fact correct in the file. I must have
made a mistake when posting, I`m sorry.
Here is a complete list of the warnings I recieve
(this time it`s correct):
************* All Branches passed integrity testing
** Warning ** Potential Node Connection Error for
object PIPE, name=COND_BP_HP1
** ~~~ ** Node Types are still UNDEFINED --
See Branch/Node Details file for further information
** ~~~ ** Inlet Node : COND_BP_HP1_IN
** ~~~ ** Outlet Node: COND_BP_HP1_OUT
** Warning ** Potential Node Connection Error for
object CHILLER:CONS COP, name=HP2
** ~~~ ** Node Types are still UNDEFINED --
See Branch/Node Details file for further information
** ~~~ ** Inlet Node : COND_HP2_IN
** ~~~ ** Outlet Node: COND_HP2_OUT
** Warning ** Potential Node Connection Error for
object PIPE, name=COND_BP_HP2
** ~~~ ** Node Types are still UNDEFINED --
See Branch/Node Details file for further information
** ~~~ ** Inlet Node : COND_BP_HP2_IN
** ~~~ ** Outlet Node: COND_BP_HP2_OUT
** Warning ** Potential Node Connection Error for
object PURCHASED:HOT WATER, name=PURCHHW
** ~~~ ** Node Types are still UNDEFINED --
See Branch/Node Details file for further information
** ~~~ ** Inlet Node : PURCHHW_IN
** ~~~ ** Outlet Node: PURCHHW_OUT
** Warning ** Potential Node Connection Error for
object COIL:WATER:SIMPLE HEATING, name=AC_HC_NE
** ~~~ ** Node Types are still UNDEFINED --
See Branch/Node Details file for further information
** ~~~ ** Inlet Node : AC_HC_IN_NE
** ~~~ ** Outlet Node: AC_HC_OUT_NE
** Warning ** Node Connection Error for object
COIL:WATER:SIMPLEHEATING, name=AC_HC_NE
** ~~~ ** Water Nodes not on any Branch or
Parent Object
** ~~~ ** Inlet Node : AC_HC_IN_NE
** ~~~ ** Outlet Node: AC_HC_OUT_NE
** Warning ** Node Connection Error for object
CHILLER:CONST COP, name=HP2
** ~~~ ** Condenser Water Nodes not on any
Branch or Parent Object
** ~~~ ** Inlet Node : COND_HP2_IN
** ~~~ ** Outlet Node: COND_HP2_OUT
** Warning ** Node Connection Error for object
PURCHASED:HOT WATER, name=PURCHHW
** ~~~ ** Hot Water Nodes not on any Branch
or Parent Object
** ~~~ ** Inlet Node : PURCHHW_IN
** ~~~ ** Outlet Node: PURCH_HW_OUT
************* There were 8 node connection errors
noted.
==============================================
AND in the .bnd file:
Component
Set,19,BRANCH,COND_BP_HP1_BR,PIPE,COND_BP_HP1,COND_BP_HP1_IN,COND_BP_HP1_OUT,UNDEFINED
...
Component Set,22,BRANCH,COND_HP2_BR,CHILLER:CONS
COP,HP2,COND_HP2_IN,COND_HP2_OUT,UNDEFINED
Component
Set,23,BRANCH,COND_BP_HP2_BR,PIPE,COND_BP_HP2,COND_BP_HP2_IN,COND_BP_HP2_OUT,UNDEFINED
...
Component Set,29,BRANCH,PURCHHW_BR,PURCHASED:HOT
WATER,PURCHHW,PURCHHW_IN,PURCHHW_OUT,UNDEFINED
...
Component Set,33,BRANCH,AC_HC_BR_NE,COIL:WATER:SIMPLE
HEATING,AC_HC_NE,AC_HC_IN_NE,AC_HC_OUT_NE,UNDEFINED
Component
Set,34,UNDEFINED,UNDEFINED,COIL:WATER:SIMPLEHEATING,AC_HC_NE,AC_HC_IN_NE,AC_HC_OUT_NE,Water
Nodes
Component Set,35,UNDEFINED,UNDEFINED,CHILLER:CONST
COP,HP2,COND_HP2_IN,COND_HP2_OUT,Condenser Water Nodes
Component Set,36,UNDEFINED,UNDEFINED,PURCHASED:HOT
WATER,PURCHHW,PURCHHW_IN,PURCH_HW_OUT,Hot Water Nodes
==============================================
Thank very much in advance for your help,
Santiago Torres
--- "Richard J. Liesen" <rliesen@xxxxxxxx> escribió:
> Hello,
> This actually looks like you mis-named the chiller
> component. The object
> name for that chiller is:
> CHILLER:CONST COP
>
> I think you are missing the T from CONST. Change
> that and see if the error
> message changes.
>
> Thanks Richard Liesen
>
> At 04:49 AM 7/1/2003, Santiago Torres wrote:
> >Hello,
> >
> >I am having problems with a simple model I adapted
> >from the DualDuctConstVolDumper example. The
> >simulation runs fine but I receive several Warnings
> >like this:
> >
> >** Warning ** Potential Node Connection Error for
> >object CHILLER:CONS COP, name=HP2
> >** ~~~ ** Node Types are still UNDEFINED --
> See
> >Branch/Node Details file for further information
> >** ~~~ ** Inlet Node : COND_HP2_IN
> >** ~~~ ** Outlet Node: COND_HP2_OUT
> >
> >and in the .bnd file:
> >
> >Component Set,22,BRANCH,COND_HP2_BR,CHILLER:CONS
> >COP,HP2,COND_HP2_IN,COND_HP2_OUT,UNDEFINED
> >
> >Could anyone please explain me what am I doing
> wrong?
> >I checked with the exaple file and everything seems
> >the same, except that I changed the node names (the
> >exaple file doesn`t produce these warnings). Must
> the
> >node names follow some kind of syntax?
> >Thank you in advance,
> >
> >Santiago.
> >
> >
>
>_________________________________________________________
> >Do You Yahoo!?
> >Información de Estados Unidos y América Latina, en
> Yahoo! Noticias.
> >Visítanos en http://noticias.espanol.yahoo.com
> >
> >
> >To unsubscribe from this group, send an email to:
> >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any
> files to the appropriate
> >folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> >Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
>
>
_________________________________________________________
Do You Yahoo!?
Información de Estados Unidos y América Latina, en Yahoo! Noticias.
Visítanos en http://noticias.espanol.yahoo.com
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx