Re: [EnergyPlus_Support] Excessive iterations
After some investigation and consulting other development team
members, we have determined that supply plenums will not work with
furnace or unitary systems, because the controls assume the supply
temperature will not change after leaving the unitary system node.
To use a supply plenum with DX cooling, use DXSystem:AirLoop which
uses setpoint managers to control the supply temperature.
Mike
On 4 Aug 2003, at 16:02, kirbyschapman wrote:
> I had a great working simulation. I then added a supply plenum, only
> to receive the dreaded "excessive HVAC iterations" warning. The supply
> plenum feeds three zones, and I was very careful to follow the supply
> plenum example. The three zones pretty much follow the setpoint
> schedule, so it seems that they are indeed receiving the conditioned
> air through the plenum.
>
> Suggestions?
>
> thanks
>
> Kirby
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Free shipping on all inkjet cartridge &
> refill kit orders to US & Canada. Low prices up to 80% off. We have
> your brand: HP, Epson, Lexmark & more.
> http://www.c1tracking.com/l.asp?cid=5510
> http://us.click.yahoo.com/GHXcIA/n.WGAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/