Purchased:Chilled Water and Purchased:Hot water simply replace a 
chiller or boiler.  You still need a complete plant loop with pump 
and controls.  See the 5ZoneAuto.idf example file.  You can also use 
the HVAC template commands "ChillerSupply1WithBypass-Autosize" and 
"BoilerSupply1WithBypass-Autosize" to set up your plant loop 
description.

If you use a variable speed pump, then you do not need a bypass.  If 
you use a constant speed pump, then you need a bypass.  It never 
hurts to include a supply bypass branch even if it is never used.

Mike



On 6 Oct 2003, at 22:57, waspoorboy wrote:

> Purchased:Chilled Water
> Purchased:Hot Water
> [I/O ref]
> When the user is not interested in a plant simulation...
> ---------------
> 
> As I tried to connect Purchased:Chilled Water to my cooling coil, from
> the error message I found that a PLANT LOOP is needed. So I put the
> Purchased Chilled Water branch onto a PLANT LOOP, Then error message
> say a PUMP is needed ?? I got a little comfused. I suspect whether
> CONNECTOR LIST, SPLITTER, MIXER, PIPE, would then also be needed too.
> 
> I'd like to know for my Purchased:Chilled Water,
> what's needed and what's not.
> 
> Do I also need to construct a bypass loop ?
> 
> Thanks,
> Ming
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for your
> HP, Epson, Canon or Lexmark Printer at MyInks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/