[EnergyPlus_Support] Re: Room is cooled (to setpoint) obviously but report gives cooling = 0
Yes, the cooling coil shows a load.
Air Loop Temperature as it should and flowrate looks ok.
But the PLANT LOOP, CoolingCoilBranch, CoolingSupplyBranch,
the flowrates are all zero. (Temperatures are correct as set.)
In other words, I have a working cooling coil which
requires no chilled water...
I also noticed that Zone/Sys Sensible Cooling Rate[W](Hourly)
has up to 10+% difference with Sensible Water Cooling Coil Rate[W]
Ming
>
> Does the cooling coil show a load?
>
> Mike
>
>
>
> > I finally got the system running.
> > [Single duct VAV, no reheat, 1 cooling coil and Purchased Chilled
> > Water only]
> >
> > The error message now become
> > SimHVAC: Maximum iterations exceeded for all HVAC loops
> > SimHVAC: Exceeding max iterations continues...350
> >
> > Output shows the room is cooled to my setpoint 21C.
> > So obviously the VAV:No Reheat cools the room,
> > or at least something cools the room.
> >
> > But the following are all ZERO, >_<
> > PURCHASEDCHILLEDWATERLOOP:Plant Loop Cooling Demand[W](Hourly)
> > PURCHASEDCHILLEDWATER#1:Purchased Cooling Rate[W](Hourly)
> > PURCHASEDCHILLEDWATER#1:Purchased Cooling Mass Flow Rate[kg/s]
> >
> > I suspect the error is in the water loop, not the air loop,
> > but no idea at all.
> >
> > Any suggestions how / where I might continue my debug ?
> >
> > Thanks again.
> > Ming
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs Online - Over 14,500 titles.
No Late Fees & Free Shipping.
Try Netflix for FREE!
http://us.click.yahoo.com/JYdFFC/XP.FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/