[EnergyPlus_Support] Re: Energy and Electricity outputs



To get the electric power of the heat pump, you must request the 
electric power output variables for each of its components:  DX 
cooling coil (DX Cooling Coil Electric Power), DX heating coil (DX 
Heating Coil Electric Power), and fan (Fan Electric Power).

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "itamargoldberger" 
<cvitamar@t...> wrote:
> I am running 3 simple Heat pumps serving 3 simple classes.
> I know the RDD file very well but I don't know which report
variable 
> to choose in order to find the electricity demand by the Heat 
> pumps.For the cooling and heating energy supplied for the room air, 
I 
> use the  zone/sys sensible heating  and cooling report/ Is this 
> correct ? 
> Another thing : I noticed that the report meter : 
> Electricity:Facility gives me a value much bigger than the sum of : 
> zone/sys sensible heating + sensible cooling + lightning. can you 
> tell me why ?
> 
> Thanks
> Itamar 



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs Online - Over 14,500 titles.
No Late Fees & Free Shipping.
Try Netflix for FREE!
http://us.click.yahoo.com/JYdFFC/XP.FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/