Re: [EnergyPlus_Support] Re: Energy and Electricity outputs
Zone/sys sensible heating/cooling are the net heating/cooling
delivered to the zone. To see the gross load on the coils, see the
DX heating/cooling coil output variables.
To see what components are included in the Electricity:Facility meter
(or any meter), look in the mtd output file. In the first section of
the file it lists every energy consumption report variable and which
meter is it connected to, in the second section of the mtd file each
meter is listed with a list of all of the component report variables
that are accumulated on that particular meter.
Mike
On 9 Oct 2003, at 15:09, donbshireyiii wrote:
> To get the electric power of the heat pump, you must request the
> electric power output variables for each of its components: DX
> cooling coil (DX Cooling Coil Electric Power), DX heating coil (DX
> Heating Coil Electric Power), and fan (Fan Electric Power).
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "itamargoldberger"
> <cvitamar@t...> wrote:
> > I am running 3 simple Heat pumps serving 3 simple classes.
> > I know the RDD file very well but I don't know which report
> variable
> > to choose in order to find the electricity demand by the Heat
> > pumps.For the cooling and heating energy supplied for the room air,
> I
> > use the zone/sys sensible heating and cooling report/ Is this
> > correct ? Another thing : I noticed that the report meter :
> > Electricity:Facility gives me a value much bigger than the sum of :
> > zone/sys sensible heating + sensible cooling + lightning. can you
> > tell me why ?
> >
> > Thanks
> > Itamar
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Rent DVDs Online - Over 14,500 titles. No
> Late Fees & Free Shipping. Try Netflix for FREE!
> http://us.click.yahoo.com/JYdFFC/XP.FAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/