Re: [EnergyPlus_Support] Window shading control with OnIfHighSolarIncident



The key is to find realistic values that are based on peoples' behavior 
patterns.  For example, you set a value for when people close the 
shades.  When do the shades get opened again?  When the sun goes behind a 
cloud or the next morning when people arrive for work?  With DOE2.1E, these 
parameters have a huge effect on how much energy DOE2 predicts will be 
saved.  You can use the following as a rough guide, depending on climate:

Daylighting control strategy:
1. On/Off: 10% lighting energy savings
2. Two or three Step dimming: 20% lighting energy savings
3. Continuous Dimming control: 30% lighting energy savings

If the simulation predicts double the savings listed above, re-check your 
assumptions.


At 13:52 19/11/2003, Frederick Winkelmann wrote:
>There is no standard value of incident solar for this type of control. I 
>recommend trying a few different values and see
>what the result is in terms of daylighting and building thermal response. 
>Or you might try optimizing this value using the
>GenOpt program (available free of charge from 
>http://SimulationResearch.lbl.gov). For example, GenOpt could be used to find
>the value that minimizes annual energy use.
>
>Fred Winkelmann
>
>leeslwong wrote:
>
> > I am going to run a commercial building with daylighting control. The
> > window shading control of OnIfHighSolarIncident is going to be used.
> > I have no idea what the recommended values (W/m2) of solar incident
> > on window are. Anyone can give me some references (i.e. books,
> > technical papers, etc.) showing the suggested figures or methods to
> > be used for my case.
> >
> > (50 W/m2 is shown in the example file of daylighting control. Is it a
> > reasonable value for the shading control?)
> >
> > Thanks
> >
> > lee
> >
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files are of the Support Web Site.
> >
> >
> >
> > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/


Chris Jones, P. Eng.
14 Oneida Avenue
Toronto, ON M5J 2E3
Tel. 416 203-7465
Fax. 416 203-8249




------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/