Re: [EnergyPlus_Support] several questions



1.  Did you include a thermostat?  Are the zone air temperatures within range?  
See the PurchAir example file.

2a.  For an interior wall with no zone on the other side, set the outside 
environment to OtherZoneSurface and specify the same surface as the other side 
object (the surface is linked to itself).  This is discussed in the I/O 
Reference.

2b. You specify ground temperatures in the input.  For the most accurate 
results, you should run the Slab program to generate monthly ground 
temperatures.  See the Auxiliary Programs document for details.

Mike

On 25 Mar 2004, at 2:55, staryhy2000 wrote:

>     I simulated the cooling loads of a building without internal 
> interference, but some results such as Zone/Sys Sensible Cooling Rate 
> and Purchased Air Sensible Cooling Rate equal to zero, why? And 
> surface ext convection coeff is about 5, whether is the number too 
> low? In report variable, which variable means cooling loads? 
>     If I want to simulate a room of a building, how should I set a 
> interwall? If the space is very large, how do I divide different 
> zones without patitionwall? Where do ground temperatures come from?
>     Thank you for your help! 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
>  -- please post any files to the appropriate folder in the Files are of the
>  Support Web Site.
> 
> 
> 
> 
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com.  Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/