Re: [EnergyPlus_Support] Question: System Sizing
Do you have ZONE SIZING objects? System sizing in EnergyPlus requires that
zone equipment also be autosized. If you have ZONE SIZING object, check the
reported zone design heating/cooling loads in the eio output file. If these
are all zero, then check you zone thermostat controls.
Mike
On 21 Apr 2004, at 11:57, zhen tian wrote:
> Hi, All:
>
> I have a question for System Sizing. Because the simulation requires system
> sizing ( I use autosize option), I setup the System Sizing. But there is always
> Error Report: " Fatal ** Air Primary Loop 1 has no air flow" in the system
> sizing. Actually all the input is similar to the Example files. So could
> someboby tell me what is pipoint problem?
>
> Thanks.
>
> David Tian
>
>
> ---------------------------------
> Do you Yahoo!?
> Yahoo! Photos: High-quality 4x6 digital prints for 25ยข
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/