"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:Many of the examples use the DUAL SETPOINT WITH DEADBAND control type with
setback/setup during unoccupied hours. With this type of control, the space
temperature is allowed to float until conditions reach the setback/setup
temperature, then there will be loads to maintain that tempeature. If you want
to completely shut off the HVAC system during unoccupied hours, then use the
system availability manager to do so. If you want to run the fans, but not
actively control the space temperature, then you can schedule off individual
components (such as the cooling or heating coils) or you can set the thermostat
control type to zero during those hours.
Mike
On 28 May 2004, at 2:18, staryhy2000 wrote:
> I want to calculate cooling/heating loads in a commercial building
> which needs control temperature on day and needn¡¯t control
> temperature at night. I find that temperature is set in 24 hours in
> example files, whether it is mean cooling loads or heating loads will
> be consumed in all time? If so ,loads will be much higher than
> practice¡¯s, won¡¯t it? If I don¡¯t want to control temperature in a
> time period of a day or in a month of a year, how should I set
> schedules?
> Thank you very much!
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups SponsorADVERTISEMENT
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
---------------------------------
Do you Yahoo!?
Friends. Fun. Try the all-new Yahoo! Messenger
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/