Sunlit area too small errors can sometimes result from using the wrong corner 
as the first vertex.  The first vertex must be consistent with the 
SurfaceStartingPosition field specified in the SurfaceGeometry object (for 
example, UpperLeftCorner).

Mike


On 2 Aug 2004, at 11:22, yutong lee wrote:

> dear all:
> when I  was simulating a building with daylightshelf , error messages apeared. I
>  compeared my IDF file with the examples , but did not find any differences.Is
> there any one can help me ? thanks in advance!
>                                         aaron lee 
> 
> 
> 
> ** Severe  ** Sunlit area too small (SHADOW)
>    **   ~~~   ** at time=00:00, for surface=NORTHRR1 WALL4
>    ** Severe  ** Sunlit area too small (SHADOW)
>    **   ~~~   ** at time=00:00, for surface=01-NORTHRR1 WALL4
>    ** Severe  ** Sunlit area too small (SHADOW)
>    **   ~~~   ** at time=00:00, for surface=02-NORTHRR1 WALL4
>    ** Severe  ** Sunlit area too small (SHADOW)
>    **   ~~~   ** at time=00:00, for surface=NORTHRR1 WALL4
> 
> 
> 
> 
> ---------------------------------
> Do You Yahoo!?
> ÃÀÅ®Ã÷ÐÇÓ¦Óо¡ÓУ¬"Ò»ËÑ"ËѱéÃÀͼ¡¢ÑÞͼºÍ¿áͼ
> 100Õ×ÓÊÏä¹»²»¹»Óã¿ÑÅ»¢µçÓÊ×ÔÖúÀ©ÈÝ£¡
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/