Without seeing the rest of the file, it is difficult to say for sure. Search
your input file for "Zone 13 Damper Inlet Node". It should appear twice, once
in the zone splitter (as shown below) and again as the inlet to the VAV
terminal unit. My guess is that it is misspelled in the VAV terminal unit, or
the terminal unit for zone 13 is missing completely.
Mike
On 6 Aug 2004, at 9:49, beyangj wrote:
> Dear,
> I have a question about node. I have define as follow;
> AIR PRIMARY LOOP,
> VAV Sys 1, !- Primary Air Loop Name
> VAV Sys 1 Controllers, !- Name: Controller List
> VAV Sys 1 Avail List, !- Name: System Availability Manager
> List
> autosize, !- Primary air design volumetric flow
> rate {m3/s}
> VAV Sys 1 Branches, !- Air Loop Branch List Name
> , !- Air Loop Connector List Name
> Air Loop Inlet Node 1, !- ReturnAir AirLoop Inlet Node
> Return Air Mixer Outlet 1, !- ZoneEquipGroup Outlet Node
> Zone Equipment Inlet Node 1, !- SupplyAirPath ZoneEquipGroup
> Inlet Nodes
> Air Loop Outlet Node 1; !- AirLoop Outlet Nodes
>
> ZONE SUPPLY AIR PATH,
> Zone Supply Air Path 1, !- Supply Air Path Name
> Zone Equipment Inlet Node 1, !- Supply Air Path Inlet Node
> Zone Splitter, !- KEY--System Component Type 1
> Splitter 1; !- Component Name 1
>
> ZONE SPLITTER,
> Splitter 1, !- Splitter Name
> Zone Equipment Inlet Node 1, !- Inlet_Node
> Zone 1 Damper Inlet Node,!- Outlet_Node_1
> Zone 2 Damper Inlet Node,!- Outlet_Node_2
> Zone 3 Damper Inlet Node,!- Outlet_Node_3
> Zone 4 Damper Inlet Node,!- Outlet_Node_4
> Zone 5 Damper Inlet Node,!- Outlet_Node_5
> Zone 6 Damper Inlet Node,!- Outlet_Node_6
> Zone 7 Damper Inlet Node,!- Outlet_Node_7
> Zone 8 Damper Inlet Node,!- Outlet_Node_8
> Zone 9 Damper Inlet Node,!- Outlet_Node_9
> Zone 10 Damper Inlet Node, !- Outlet_Node_10
> Zone 11 Damper Inlet Node, !- Outlet_Node_11
> Zone 12 Damper Inlet Node, !- Outlet_Node_12
> Zone 13 Damper Inlet Node, !- Outlet_Node_13
> Zone 14 Damper Inlet Node, !- Outlet_Node_14
> Zone 15 Damper Inlet Node, !- Outlet_Node_15
> Zone 16 Damper Inlet Node; !- Outlet_Node_16
>
> But the complier gave the Severe message: Node ZONE 13 DAMPER INLET
> NODE connects to no component, Occurs in Supply Air Path=ZONE SUPPLY
> AIR PATH 1. I have checked many times, and I can't find the problem.
> Could you help me?
>
> Thanks in advance
>
> Stewart
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/