The controller convergence tolerance values are specific to EnergyPlus, you 
will not find any technical literature discussing these.  The value here 
depends on the type of equipment you are using.  Some tolerances are DeltaC, 
some are fraction of load.  The default values are reasonable, or you may 
choose to use smaller numbers.  I would not use anything larger than the 
defaults.

Item 1 implies that you are using COIL:Water:SimpleCooling.  Due to limitations 
in this model, it is being phased out.  For a study focusing on humidity 
control, I would strongly recommend upgrading for EnergyPlus 1.2.1 (released 
yesterday) and using the new COIL:Water:Cooling or using 
COIL:Water:DetailedFlatCooling.

Mike


On 4 Oct 2004, at 18:37, hjunmoon wrote:

> 
> Dear all,
> 
> I am doing a sensitivity analysis with humidity control. To do this, 
> I have to set an appropriate ranges of the parameters related to the 
> control of heating/cooling coils.
> 3 parameters are in question:
> 1) Leaving relative humidity from cooling coil
> 2) Heating coil: Controller convergence tolerance
> 3) Cooling coil: Controller convergence tolerance
> 
> Can anyone give references which give typical ranges of these 
> parameters? Any papers, manuals, websites, reports related to these 
> parameters are welcome. I would like to work on as many as 
> references I can get. Thanks in advance.
> 
> Best Regards,
> 
> HJ Moon
> Georgia Institute of Technology
> gt6102a@xxxxxxxxxxxxxxx
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/