My apologies for the delay in responding.  When I run the uploaded file, the 
columns which were zero in the original request (OPTTest_fivZonDXVAV.xls) now 
show significant loads.  What version of EnergyPlus are you running?  I ran 
OPT512.10_fivZonDXVAV.idf with version 1.2.1.022.

Mike


On 25 Feb 2005, at 9:54, Ali_Ajmi wrote:

> 
> 
> I would agree that there is a problem in the thermostat control or/and supply
> air set point control (but i don't know how to fix it). The system used here is
> DX cooling coil VAV with reheat (gas). Please have a look to the the IDF file
> which is uploaded under name OPT512.10_fiveZoneDXVAV.
> 
> 
> Regards
> Ali
> 
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> 
> It is hard to tell what may be happening without seeing the input file. Some
> thoughts:
> 
> 1. The zone temperatures seem reasonable and there are large cooling loads for
> all hours. Perhaps there is an error in the internal gains inputs (lights,
> electric equipment, etc.)?
> 
> 2. Check thermostat controls and supply air set point controls.
> 
> 3. What type of system is this?
> 
> Mike
> 
> 
> On 24 Feb 2005, at 14:54, Ali_Ajmi wrote:
> 
> > 
> > Dear All,
> > Could any explain why i have zero coulmn of North, South and Interior and also
> > Main Heating Coil DX1 (all these coulmn are higliated in red). This file is
> > uploaded under name OPTTest_fiveZoneDXVAV in the group files folder at this
> > link (http://groups.yahoo.com/group/EnergyPlus_Support/files/).
> > 
> > Thanks
> > Ali
> > 
> > 
> > ---------------------------------
> > ALL-NEW Yahoo! Messenger - all new features - even more fun! 
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support 
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> ---------------------------------
>  ALL-NEW Yahoo! Messenger - all new features - even more fun!  
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/