[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Inexplicable output data
My apologies for the delay in responding. When I run the uploaded file, the
columns which were zero in the original request (OPTTest_fivZonDXVAV.xls) now
show significant loads. What version of EnergyPlus are you running? I ran
OPT512.10_fivZonDXVAV.idf with version 1.2.1.022.
Mike
On 25 Feb 2005, at 9:54, Ali_Ajmi wrote:
>
>
> I would agree that there is a problem in the thermostat control or/and supply
> air set point control (but i don't know how to fix it). The system used here is
> DX cooling coil VAV with reheat (gas). Please have a look to the the IDF file
> which is uploaded under name OPT512.10_fiveZoneDXVAV.
>
>
> Regards
> Ali
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
>
> It is hard to tell what may be happening without seeing the input file. Some
> thoughts:
>
> 1. The zone temperatures seem reasonable and there are large cooling loads for
> all hours. Perhaps there is an error in the internal gains inputs (lights,
> electric equipment, etc.)?
>
> 2. Check thermostat controls and supply air set point controls.
>
> 3. What type of system is this?
>
> Mike
>
>
> On 24 Feb 2005, at 14:54, Ali_Ajmi wrote:
>
> >
> > Dear All,
> > Could any explain why i have zero coulmn of North, South and Interior and also
> > Main Heating Coil DX1 (all these coulmn are higliated in red). This file is
> > uploaded under name OPTTest_fiveZoneDXVAV in the group files folder at this
> > link (http://groups.yahoo.com/group/EnergyPlus_Support/files/).
> >
> > Thanks
> > Ali
> >
> >
> > ---------------------------------
> > ALL-NEW Yahoo! Messenger - all new features - even more fun!
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
>
>
>
> ---------------------------------
> ALL-NEW Yahoo! Messenger - all new features - even more fun!
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/