Re: [EnergyPlus_Support] About the 5zoneAirCooled example
You can just take the Zone Sizing object for PLENUM-1 out. It is not
being used in the
sizing calculation.
But this raises the issue - what effect do plenums have on the
calculation of zone design
air flow rates? The answer can not be found without a sophisticated
iterative sizing procedure,
which EnergyPlus doesn't have. This is a 1 story building with a return
plenum in contact with
the flat roof. On a summer design day, there will be a large roof load
which will mainly effect the
plenum return air temperature; some of this roof load will be exhausted,
some will appear as a
load on the cooling coil. The question is how to deal with this in the
sizing calculation. I ended
up deciding to treat the plenum as an unconditioned space in the sizing
calculation. This is a conservative
decision - it will cause an overestimate of the conditioned spaces'
design cooling flow rates, but
will do a decent job of sizing the coil. By the way, this case is one of
the more extreme examples of
return plenum's influence on conditoned zone loads. For a mid-floor in a
multi-story building, the
influence of a plenum on zone loads is quite small.
Fred Buhl
energypluser wrote:
>Dear all,
>
> When I simulate the 5zoneAirCooled with its default input, a
>warning message shows up as follow:
> ** Warning ** Requested Sizing for Zone="PLENUM-1", Zone is not
>found in the Controlled Zones List.
>
> Does it have some influnence upon the simulation results ?How
>can I fix it up ?
> 3x in advance
> charlie
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/