RE: [EnergyPlus_Support] the low-e glass




hi, 
 
I think there a couple of points you should understand about low-e glass.  First, the glass itself is opaque to the long wave and the low-e coating is used to suppress heat transfer across the gap between the glass.  So the longwave radiation from interior surfaces and objects is blocked before it gets to the low-e coating.  Second, there are many types of low-e and there is an important distinction between high solar gain version and low-solar gain versions.   What you describe below can be true for high-solar-gain low-e but not necessarily for low-solar-gain low-e.   EnergyPlus is a great tool for deciding what types of low-e of window are best for each face of the building.  Check out the Window 5.2 computer program from LBNL for details about window performance.  
 
Brent

-----Original Message-----
From: princeps7405 [mailto:princeps11@xxxxxxxxxxx]
Sent: Wednesday, April 06, 2005 8:27 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] the low-e glass



Dear all

I have got many solutions on e+ from yours for long time.

this is not a question for e+ and energy simulation but a general 
concept to select glazing.


I make a office model for energy simualtion. It has a high internal 
loads such as occupant, lightings and office automation. The window-
wall ratio is bigger than 90%. 

I think that a double low-e glass(6mmLE/24mm-Air/6mmCL) is much 
benefit 
than a doule pain glass(6mmCL/24mm-Air/6mmCL) when it is installed 
where internal load is a low-level and heating is prior to cooling 
such 
as residental house needed to air conditioning at night.

Because of its low emittance of long wave radiation, some people say 
that the low-e glass may have disadvatage at west or south perimeter 
zone of an office, transmitted short wave radiation of sun and 
generated much long wave radiation by occupants, lightings and OA 
machines.

Although there are a high internal load and long solar heat gian time,
Is a double low-e glass the best choice for the west and south face 
of office building?

Have you exprienced to simulate that case?

or Do you have a related information for the selecting windows 
according 
to its internal condition and face directions.

i'm waiting advices of yours.

thanks






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




  _____  

Yahoo! Groups Links


*	To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
  

*	To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
  

*	Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 




[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/