Re: [EnergyPlus_Support] About the heating load



What type of system is this for?  Are there other heating coils such as reheat 
coils?  Are the zone setpoints being maintained?  Check the inputs in the 
SYSTEM SIZING object.  Coil sizing is determined by the specified supply air 
temperatures, the system flow rate, and the mixed air temperature at the design 
load condition.

Mike


On 29 Apr 2005, at 8:55, beyangj wrote:

> Dear,
> There was a warning in the ERR file as follow:
> ** Warning ** The design coil load is zero for 
> COIL:Water:SimpleHeating MAIN HEATING COIL 1
>    **   ~~~   ** The autosize value for max water flow rate is zero
>    **   ~~~   ** To change this, input a value for UA, change the 
> heating design day, or lower
>    **   ~~~   **   the system heating design supply air temperature
> 
> I don't know why this happened. I changed the heating design day, 
> but it didn't work,and it gave the same warning message. And the 
> Heating:Electricity [J](RunPeriod) in the Meter file wasn't zero, it 
> was 3.90248E+12J, and the heating load is correct in this case? 
> Thanks in advance!
> 
> Best,
> 
> Stewart
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/