Re: [EnergyPlus_Support] Daylight detailed model



That should work, but this may cause the lights to never shut off completely 
when using control type 3 (continous/off).  I would recommend reporting the 
"Ltg Power Multiplier from Daylighting" at the hourly or timestep frequency to 
verify that the controls are behaing as you expect.  

I cannot answer about the behavior of actual equipment.  My guess is that you 
are correct that the dimming can only proceed to a certain minimum level.  That 
is why control type 3 exists to stop dimming at a certain point and then if the 
daylighting is adequate to simply shut off power completely to the lights.

Mike


On 1 May 2005, at 15:26, Fábyo Luiz Pereira wrote:

>    Dear all,
> 
>    I'm doing a daylight detailed model and have a question:can I use a "Minimum
> Input Power Fraction for Continuous Dimming Control" and a "Minimum Light Output
> Fraction for Continuous Dimming Control" equals to zero?
> 
>    I do this question because I'm modeling fluorescent lamps and don't know if
> its power can be continuously dimmerized until zero.
> 
>    Thanks.
> 
> ________________________________________________________
>  Engº Fábyo Luiz Pereira
>  UFRGS - Laboratório de Vapor e Refrigeração
>  Rua Sarmento Leite, 425 - Sala 203 - Centro - 90050-170
>  Fone / Fax: +55 51 3316-3167 / 3316-3355
>  www.mecanica.ufrgs.br/lafrig
>  Porto Alegre - RS - BRASIL
> 
> 
> 
> 
> 
> Yahoo! Acesso Grátis - Internet rápida e grátis. 
> Instale o discador agora! http://br.acesso.yahoo.com/
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/