[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Re: About the evaporator outlet temp of electric chiller
Hi Charlie,
You can control the leaving temperature of the chiller using the component set point based control. Please refer to the CompSetPtControl.idf test file. EnergyPlus currently does not have the capability to control the chilller outlet temperature float within a dead band.
Thanks
Sankar
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of applezealot
Sent: Thu 5/19/2005 7:57 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: About the evaporator outlet temp of electric chiller
Dear Mike
Could please tell me some methods to controll the leaving
temperature of chiller and let it float in a range.
Thank you in advance.
charlie
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> With dual setpoints, EnergyPlus would use the upper setpoint to
control
> chillers, and the lower setpoint to control boilers. EnergyPlus
will not
> control chillers to float within a range as described below.
>
> Mike
>
>
> On 12 May 2005, at 6:39, energypluser wrote:
>
> > Dear all:
> >
> > I set the chiller evaporator outlet node for the Loop
Temperature
> > Setpoint Node in Plant-Condenser Loops. And the setpoint manager
for
> > this node is a dual setpoint manager with the low and high
scheduled
> > temperature at 7C and 13C for all days respectively.
> > The purpose of using this setpoint manager is to let the
chilled
> > water outlet temperature varies between the deadband. But the
> > simulation results show that the chiller supply temperature is
10C,
> > which is the average value of the upper and lower temperature
limit.
> > Is E+ able to control the chiller water supply temperature in
this
> > way?
> > Thank you in advance!
> >
> > charlie
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/