[EnergyPlus_Support] Re: QUESTION ON AIR COOLED CONDENSER INLET TEMPERATURE



Hi, Richard,

Thanks for your response. Actually I am not really operating the 
chiller in cold days. Right now I am just running the file for winter 
and summer design days, in order to get the auto-sizing information. 
I am hoping there is be no such warning when I do the entire year 
simulation. 

Thanks again,
Chaoqin


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
<RRaustad@F...> wrote:
> Why is your chiller operating on such a cold day?
> 
> Air-cooled chillers should not be used in cold climates without 
freeze 
> protection. Energyplus does not currently support freeze protection 
on 
> electric chillers. If you want to continue to use the air-cooled 
> electric EIR chiller, limit the minimum outdoor temperature in the 
> Cooling Capacity Function of Temperature Curve and Energy Input to 
> Cooling Output Ratio Function of Temperature Curve objects to 0C 
and 
> verify that the output makes sense (i.e. Capacity and Power at this 
low 
> temperature is reasonable). Limiting the minimum outdoor 
temperature 
> "caps" the capacity and power at 0C and simulates the use of 
heaters to 
> maintain chiller performance. This heater power will not be 
accounted 
> for in the simulation. If the output makes sense you can disregard 
the 
> warnings. Otherwise change to a water cooled chiller where the 
entering 
> condenser water temperature can be better controlled.
> 
> zhaicq98 wrote:
> 
> > Hi,
> >
> > I am simulating a system with an air-cooled electric chiller. 
However I
> > got lots of warning messages, saying:
> >
> > ElectricEIRChillerModel:Air Cooled Condenser Inlet Temperature 
below 0C
> >
> > What should I to with regard to these warnings? I am using the 
chiller
> > in a relatively cold climate.
> >
> > Thanks,
> > Chaoqin
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
> > appropriate folder in the Files area of the Support Web Site.
> >
> >
> >
> >
> > SPONSORED LINKS
> > Scheduling program software 
> > <http://groups.yahoo.com/gads?
t=ms&k=Scheduling+program+software&w1=Scheduling+program+software&w2=C
onstruction+software+program&w3=Payroll+software+program&w4=Accounting
+software+program&w5=Affiliate+program+software&w6=Program+management+
software&c=6&s=196&.sig=22tSUUIr5-y7NpdZEjRKyA> 
> > 	Construction software program 
> > <http://groups.yahoo.com/gads?
t=ms&k=Construction+software+program&w1=Scheduling+program+software&w2
=Construction+software+program&w3=Payroll+software+program&w4=Accounti
ng+software+program&w5=Affiliate+program+software&w6=Program+managemen
t+software&c=6&s=196&.sig=jiIsH46YluTFGHTIjOuzOw> 
> > 	Payroll software program 
> > <http://groups.yahoo.com/gads?
t=ms&k=Payroll+software+program&w1=Scheduling+program+software&w2=Cons
truction+software+program&w3=Payroll+software+program&w4=Accounting+so
ftware+program&w5=Affiliate+program+software&w6=Program+management+sof
tware&c=6&s=196&.sig=bpandTL_9PlIAsB2jxqmFQ> 
> >
> > Accounting software program 
> > <http://groups.yahoo.com/gads?
t=ms&k=Accounting+software+program&w1=Scheduling+program+software&w2=C
onstruction+software+program&w3=Payroll+software+program&w4=Accounting
+software+program&w5=Affiliate+program+software&w6=Program+management+
software&c=6&s=196&.sig=l_rKIv6738s-oIrC1oXsng> 
> > 	Affiliate program software 
> > <http://groups.yahoo.com/gads?
t=ms&k=Affiliate+program+software&w1=Scheduling+program+software&w2=Co
nstruction+software+program&w3=Payroll+software+program&w4=Accounting+
software+program&w5=Affiliate+program+software&w6=Program+management+s
oftware&c=6&s=196&.sig=HsTX1ptWm-Hsew69JVLPdw> 
> > 	Program management software 
> > <http://groups.yahoo.com/gads?
t=ms&k=Program+management+software&w1=Scheduling+program+software&w2=C
onstruction+software+program&w3=Payroll+software+program&w4=Accounting
+software+program&w5=Affiliate+program+software&w6=Program+management+
software&c=6&s=196&.sig=LhdBC2v67EnHO-xmRhW6Uw> 
> >
> >
> >
> > ------------------------------------------------------------------
------
> > YAHOO! GROUPS LINKS
> >
> >     *  Visit your group "EnergyPlus_Support
> >       <http://groups.yahoo.com/group/EnergyPlus_Support>" on the 
web.
> >        
> >     *  To unsubscribe from this group, send an email to:
> >        EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
subject=Unsubscribe>
> >        
> >     *  Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> >       Service <http://docs.yahoo.com/info/terms/>.
> >
> >
> > ------------------------------------------------------------------
------
> >
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
> 
> 
> 
> [Non-text portions of this message have been removed]




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/