[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Purchase Air problem 2
Dear Mike,
I would like to refer to an example day, 7th Jan.
For LVG zone, the Heating Thermostat is set to 20C (Control Type 1) during hours 9-11, 13, 14, 19-23.
However, the LVG MAT does not show 20C except for hours 22 and 23 (19C, 21C, 24C, 34C, 36C, 25C, 23C, 22C).
Even the supply air temperature (Node2) does not show the purchase air supply air temperature, which was set to 40C.
For the same day, ADJ zone MAT meets all set point temperature, and the supply air temperature also shows the expected
value, 50C.
The same happens to ADJ zone during cooling period, for example, 2nd July.
ADJ MAT is 20, 24, 25, 25, 26 for hours 1 -7, though the cooling setpoint is 28.
The supply air node (NodeB) also did not show the expected value, 13C for those hours,
although Control Type is 2 and Setpoint shows 28C.
I hope this explains my confusion.
Please advice and thank you!
PuiWah
こんにちは。
In message "Re: [EnergyPlus_Support] Purchase Air problem 2",
Michael J. Witte wrote...
>My results look the same as yours. Whenever the control type is set to zero,
>the setpoint will not be met, because the thermostat is off. There are times
>when the zone is warmer than the heating setpoint or cooler than the cooling
>setpoint, but that does not mean the system is not meeting setpoint.
>
>If you want to maintain the space temperature at all times, then use the DUAL
>SETPOINT WITH DEADBAND thermostat control type, so that the system can
>automatically switch between heating and cooling as needed.
>
>If this still does not explain things, please refer to specific times in the
>output file in which you see a problem.
>
>Mike
>
>
>On 26 Jul 2005, at 22:52, wah wrote:
>
>> Dear Mike,
>>
>> Thank you for the advice.
>>
>> The Heating and Cooling Setpoint and Control Type do show up as expected.
>> However, the LVG MAT could not meet Heating Setpoint but meet Cooling Setpoint,
>> while ADJ MAT meets both setpoints most of the time.
>>
>> I used the PurchAir Problem idf with JPN_Osaka_IWEC.epw weather file.
>> As you mentioned the purchased air is meeting the request, I wonder if we are
>> getting the same output files.. I uploaded my output file:
>> PurchaseAirProbSpreadsheet Random check shows LVG Purchase Air meets 36% of
>> Heating and 100% of Cooling requirement;
>> ADJ Purchase Air meets 96% if Heating and 66% of Cooling
>> requirement
>> I suppose if everything goes well the Heating and Cooling requirement should be
>> met at least 80% of the time?
>>
>> Please advice and thank you!
>>
>> PuiWah
>>
>>
>> こんにちは。
>>
>> In message "Re: [EnergyPlus_Support] Purchase Air problem",
>> Michael J. Witte wrote...
>> >Add the following report variables to see how the system controls are
>> operating: > > Zone/Sys Thermostat Heating Setpoint > Zone/Sys Thermostat
>> Cooling Setpoint > Zone/Sys Thermostat Control Type > >Reviewing the results
>> shows that the purchased air is meeting these requests. >In the control type
>> schedules there are several months where the control type >is being set to zero
>> which means no heating or cooling should operate. > >Mike > > >On 25 Jul 2005,
>> at 15:31, 黄佩華 wrote: > >> Hello. >> I am using Purchase Air but it
>> does not work consistently. >> The Zone MAT meet the setpoint temperature only
>> during some days in the >> heating and cooling period. >> Uploaded the file:
>> PurchAir Problem >> Could anybody please advice whether it is problem with my
>> setting? >> Thank you! >> >> PuiWah >> >> >> >> >> The primary EnergyPlus web
>> site is found at: >> http://www.energyplus.gov >> >> The group web site is: >>
>> http://groups.yahoo.com/group/EnergyPlus_Support/ >> >> Attachments are not
>> allowed -- please post any files to the appropriate folder >> in the Files area
>> of the Support Web Site. >> >> Yahoo! Groups Links >> >> >> >> >> >> >> >> > >
>> > >======================================================== >Michael J. Witte,
>> GARD Analytics, Inc. >EnergyPlus Testing and Support
>> >EnergyPlus-Support@xxxxxxxx > > > > >The primary EnergyPlus web site is found
>> at: >http://www.energyplus.gov > >The group web site is:
>> >http://groups.yahoo.com/group/EnergyPlus_Support/ > >Attachments are not
>> allowed -- please post any files to the appropriate folder in the Files area of
>> the Support Web
>> Site.
>> >
>> >
>> >
>> > YAHOO! GROUPS LINKS
>> > Visit your group "EnergyPlus_Support" on the web.
>> > To unsubscribe from this group, send an email to:
>> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>> > Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>> >
>>
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the appropriate folder
>> in the Files area of the Support Web Site.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>>
>>
>
>
>
>========================================================
>Michael J. Witte, GARD Analytics, Inc.
>EnergyPlus Testing and Support
>EnergyPlus-Support@xxxxxxxx
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web
Site.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12hov8q6u/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1122633957/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/">In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/