Re: [EnergyPlus_Support] Voids between zones again!



That's a fairly good summary of the situation. My comments are:

a) windows should be used only if there is significant short-wave 
radiation expected to pass between
the 2 zones. Windows will not transmit long wave radiation.

b) It is true that surfaces in adjacent zones will not "see" each other 
in the long wave spectrum. But this is
not as significant as it seems - a light or R-value wall between 2 zone, 
with high IR absorbtivity on both
sides, will do a good job of absorbing IR in one zone and transmitting 
it (via conduction and reradiation) to
the adjacent zone. Of course in most situations, with both zones 
conditioned, such a transfer is
inconsequential.

Fred Buhl

Clarice Bleil de Souza wrote:

>Hi everybody,
> 
>I've been reading all the answers about voids between zones and I still couldn't decide which is the best way to model this kind of surface. Just to double check what I understood from all the replies I've listed what happens with each modelling choice:
> 
>1) NO surfaces:
>- NO heat exchange
>- NO mass exchange (it is necessary to use mixing mode to account for it)
>- NO long wave heat exchange between surfaces in different zones
>- NO solar gains passing from one zone to the other
> 
>2) R - value:
>- NO mass exchange
>- NO solar gains (because the surface is opaque) could I specify it as transparent playing around with the absorptance values? Or E+ need transmittance values to understand that sunbeams are passing through the surface
>- No long wave heat exchange
> 
>3) Window
>- Heat exchange
>- Solar gains
>- NO mass exchange
>- How about longwave radiation between zones?
> 
>Apparently, the best way to model is using a window with a low resistance so that E+ understand that the surface is transparent, and then consider solar gains between zones, as well as accounts for heat transfer between the zones. However, I would appreciate your opinion again on the matter as it seems to be quite complex.
> 
>Thank you very much for the help again and hope hearing from you soon
> 
>Best regards,
> 
>Clarice
>
>		
>---------------------------------
>Yahoo! Acesso Grátis: Internet rápida e grátis. Instale o discador agora!
>
>[Non-text portions of this message have been removed]
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>  
>


------------------------ Yahoo! Groups Sponsor --------------------~--> 
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12hgaqr42/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1124140957/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/";>In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/