Re: [EnergyPlus_Support] Can I use COMIS model and Ventilation at the same time?
When the COMIS air flow model is active, the Simple air flow model objects
(VENTILATION, INFILTRATION, MIXING, and CROSS-MIXING) are inactive. It is one
or the other, but never both types together. To add a constant airflow to a
COMIS model, use COMIS AIR FLOW:Crack with a value of zero for "Air mass flow
exponent". This should result in a constant air flow through the crack, thus
simulation the exhaust fan. I believe you would also need to associate an
appropriate node and pressure with this crack to force the direction of flow.
Mike
On 3 Nov 2005, at 4:49, winterwizardcn wrote:
> Hello Team:
>
> I am trying to simulate natural ventilation effect of a deep room
> with both side windows. In order to facilitate air flow in the room,
> there is a exhaust fan inside of the room. Can I use COMIS modul as
> well as ventilation at the same time? If not, what is the best way to
> modle that?
>
> Thanks,
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/