Re: [EnergyPlus_Support] multiplier
1. The multiplier multiplies all zone-level loads, including the load passed
to the HVAC system. If the fancoils are autosized, they will size to the 20x
load. If the fancoils and other HVAC equipment are not autosized, you must
specify them at 20x.
2. If all floors are controlled to the same temperature, then it would seem
the heat recovery result would be identical with either approach.
Mike
On 29 Nov 2005, at 6:34, Clarice Bleil de Souza wrote:
> Hi everybody,
>
> Thanks a lot for the reply about the controllers Mike!
>
> Just another quick question. The multiplier field in the zone group is used to
> multiply just the zone not the system is that correct? If I have a 20 storey
> residential building with typical floors and consequently typical zones each
> one being coolled by a fancoil unit when I set a value in the multiplier it
> will only multiply the zone loads not the fancoils, right? How do I "multiply"
> the fancoils so that I account for the energy consumption of the whole
> building?
>
> I was thinking to work floor by floor and then simply multiply everything at
> the end but I have a heat recovery unit in the roof of the building that
> treats all fresh air coming into the zones so I don't think work floor by
> floor will give me the correct result. Can anybody give me a light on that?
>
> Thanks a lot again for the help
>
> Regards,
>
> Clarice
>
>
> ---------------------------------
> Yahoo! doce lar. Faça do Yahoo! sua homepage.
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
AIDS in India: A "lurking bomb." Click and help stop AIDS now.
http://us.click.yahoo.com/9QUssC/lzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/