[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Plant loop objects
There is another option. EnergyPlus can do primary-secondary loops, see
example file TermReheatPri-SecLoop.idf The object which connects the primary
and secondary loops is called CONNECTION COMPONENT:PLANTLOOP.
What you describe is basically a single primary loop with multiple secondary
loops. Theoretically, one could have several CONNECTION COMPONENT:PLANTLOOP
objects in parallel on the demand side of the primary hot water loop. But I
don't know that anyone has ever tried simulation more than one secondary loop.
It might fail.
The bigger question is how are the zones controlled. Once the pump for a group
of rooms is on, are there individual control valves in each room? Is this just
a pumping power issue?
Mike
On 28 Feb 2006 at 8:20, Richard Raustad wrote:
> There is a difference between a simulation and a real world application.
> The simulation strives to simplify the characteristics of a real world
> application in order to simplify the inputs. In EnergyPlus, pumps are
> considered plant equipment and must be installed on the plant supply
> side of the loop. There are only minor differences in pump energy when
> considering a single pump serving multiple branches and multiple pumps
> serving individual branches, so here you see the simplification used to
> minimize the input requirements for this type of water loop.
>
> From the Eng. Ref. for Pumps:
>
> The water pump is quite simply the component that drives the flow. How
> it reacts depends on several different conditions. In total, there are
> three different decision variables, two of which are defined by user
> input. These three deciding factors are whether the pump is constant or
> variable speed, whether the pump operation is continuous or
> intermittent, and whether or not there is a load on the loop. The pump
> is simulated first on the supply side loop after the demand side loop
> has determined what the demand on the loop will be. For further
> reference look at sections Pump Control for Plant and Condenser Loops,
> Plant/Condenser Supply Side, and Plant/Condenser Demand Side in the
> Plant Flow Resolver of the Engineering Document.
>
>
>
> Tony Baxter wrote:
>
> > Richard,
> >
> > Thanks for the response to use a single plant loop.
> > There is a problem using a single pump on the supply side, as this
> > would not
> > represent a real situation where each group of rooms had its own pump.
> >
> > I am trying to represent a zoned heating system. We use individual
> > rooms as
> > Eplus zones. Our groups of rooms would each have a pump, then these main
> > demand side pipes (each with a pump) would all be joined together to be
> > served by the single plant object, as you have advised.
> >
> > Is it ok to have pumps on the demand side?
> >
> > Thanks for your advice so far.
> >
> > Tony Baxter
> >
> >
> >
> >
> >
> > -----Original Message-----
> > From: Richard Raustad [mailto:RRaustad@xxxxxxxxxxxx]
> > Sent: 27 February 2006 19:26
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: Re: [EnergyPlus_Support] Plant loop objects
> >
> >
> > Use a single plant loop and a single variable speed pump connected to
> > the inlet of the plant (supply) side of the loop. All heating coils will
> > be connected using splitters and mixers on the equipment (demand) side
> > of the loop. Bypass pipes are recommended as a precaution for all water
> > loops (one bypass pipe on the supply and one on the demand side of a
> > water loop). There will be no flow through the demand side bypass pipe
> > when using INTERMITTENT control for variable speed pumps as long as the
> > water flow rate is above the minimum flow rate specified for the pump.
> > There will be no flow rate through the supply side bypass pipe unless
> > the demand side water flow rate is greater than the maximum water flow
> > rate specified for the boiler. Draw a simple schematic of your hot water
> > loop and it will become very clear when you would require bypass pipes.
> > There are many example files (5Zone*.idf and many others) that show the
> > proper connection for a hot water plant.
> >
> > tonybaxterhevacomp wrote:
> >
> > > Hello all,
> > >
> > > I am using groups of rooms, each room having a heating coil on a
> > > branch. Each group of rooms is connected via a splitter and mixer and
> > > has a pump. I have several of these groups, all served by the same
> > > plant boiler.
> > >
> > > The question is, do I need one Plant loop per room group (in which
> > > case, how do I join plant loops to serve them all from the same boiler)
> > > OR do I have one Plant loop for the boiler (in which case do I join the
> > > room groups - with another higher level splitter, mixer?)
> > >
> > > Many thanks
> > >
> > > Tony Baxter
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > > appropriate folder in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> > > press the "search" button.
> > >
> > >
> > >
> > >
> > > SPONSORED LINKS
> > > Cad software program
> > >
> > <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Cad+software+pr
> >
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Cad+software+pr>
> >
> ogram&w2=Email+software+program&w3=Medical+software+program&w4=Backup+softwa
> >
> re+program&w5=Wedding+program+software&w6=Maintenance+program+software&c=6&s
> > =177&.sig=BFI_n2cYW__VOz-DP-LcGg>
> > > Email software program
> > >
> > <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Cad+software+
> >
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Cad+software+>
> >
> program&w2=Email+software+program&w3=Medical+software+program&w4=Backup+soft
> >
> ware+program&w5=Wedding+program+software&w6=Maintenance+program+software&c=6
> > &s=177&.sig=f865WzxIHHYjchHhNlWwlQ>
> > > Medical software program
> > >
> > <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Cad+softwar
> >
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Cad+softwar>
> >
> e+program&w2=Email+software+program&w3=Medical+software+program&w4=Backup+so
> >
> ftware+program&w5=Wedding+program+software&w6=Maintenance+program+software&c
> > =6&s=177&.sig=faA1gfRfwe6W-yJUEymjuA>
> > >
> > > Backup software program
> > >
> > <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Cad+software
> >
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Cad+software>
> >
> +program&w2=Email+software+program&w3=Medical+software+program&w4=Backup+sof
> >
> tware+program&w5=Wedding+program+software&w6=Maintenance+program+software&c=
> > 6&s=177&.sig=Cmscwy21WzrxVXw4jC0HpQ>
> > > Wedding program software
> > >
> > <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Cad+softwar
> >
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Cad+softwar>
> >
> e+program&w2=Email+software+program&w3=Medical+software+program&w4=Backup+so
> >
> ftware+program&w5=Wedding+program+software&w6=Maintenance+program+software&c
> > =6&s=177&.sig=ckPkVufKwCY2o9tsWrlnXQ>
> > > Maintenance program software
> > >
> > <http://groups.yahoo.com/gads?t=ms&k=Maintenance+program+software&w1=Cad+sof
> >
> <http://groups.yahoo.com/gads?t=ms&k=Maintenance+program+software&w1=Cad+sof>
> >
> tware+program&w2=Email+software+program&w3=Medical+software+program&w4=Backu
> >
> p+software+program&w5=Wedding+program+software&w6=Maintenance+program+softwa
> > re&c=6&s=177&.sig=BcCn-ontknprdFYInW_UGA>
> > >
> > >
> > >
> > > ------------------------------------------------------------------------
> > > YAHOO! GROUPS LINKS
> > >
> > > * Visit your group "EnergyPlus_Support
> > > <http://groups.yahoo.com/group/EnergyPlus_Support>" on the web.
> > >
> > > * To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> >
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
> > >
> > > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > > Service <http://docs.yahoo.com/info/terms/>.
> > >
> > >
> > > ------------------------------------------------------------------------
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> > the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> > press the "search" button.
> >
> >
> >
> >
> > SPONSORED LINKS
> > Backup software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Backup+softwar
> e+program&w2=Medical+software+program&w3=Cad+software+program&w4=Email+softwar
> e+program&w5=Maintenance+program+software&w6=Wedding+program+software&c=6&s=17
> 7&.sig=qmnzUUStgtVYGlcaQt3yMw>
> > Medical software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Backup+softwa
> re+program&w2=Medical+software+program&w3=Cad+software+program&w4=Email+softwa
> re+program&w5=Maintenance+program+software&w6=Wedding+program+software&c=6&s=1
> 77&.sig=BYpa4SYprSR4IAo58Jsyog>
> > Cad software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Backup+software+p
> rogram&w2=Medical+software+program&w3=Cad+software+program&w4=Email+software+p
> rogram&w5=Maintenance+program+software&w6=Wedding+program+software&c=6&s=177&.
> sig=Fa0wmbfF7LsZ7FduljC76g>
> >
> > Email software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Backup+software
> +program&w2=Medical+software+program&w3=Cad+software+program&w4=Email+software
> +program&w5=Maintenance+program+software&w6=Wedding+program+software&c=6&s=177
> &.sig=IEcMpEZSYjjfiWraURVKjQ>
> > Maintenance program software
> >
> <http://groups.yahoo.com/gads?t=ms&k=Maintenance+program+software&w1=Backup+so
> ftware+program&w2=Medical+software+program&w3=Cad+software+program&w4=Email+so
> ftware+program&w5=Maintenance+program+software&w6=Wedding+program+software&c=6
> &s=177&.sig=7jOsrOrnfA-UF06JGXavCA>
> > Wedding program software
> >
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Backup+softwa
> re+program&w2=Medical+software+program&w3=Cad+software+program&w4=Email+softwa
> re+program&w5=Maintenance+program+software&w6=Wedding+program+software&c=6&s=1
> 77&.sig=iFVpuXovWt8O6m4VzTrdTg>
> >
> >
> >
> > ------------------------------------------------------------------------
> > YAHOO! GROUPS LINKS
> >
> > * Visit your group "EnergyPlus_Support
> > <http://groups.yahoo.com/group/EnergyPlus_Support>" on the web.
> >
> > * To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
> >
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service <http://docs.yahoo.com/info/terms/>.
> >
> >
> > ------------------------------------------------------------------------
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/