Hello all,

I would greatly appreciate any input with a system that requires 
tight RH control. I am having difficulty with an AHU which is 
comprised of 

Mixing box -> Coiling Coil -> Humidifier -> Fan ->-------------------
-reheat units -> zone

I am trying to undertake a simulation for an Art Gallery. 
Accordingly, I required tight RH control. At this stage in the 
simulation, I would like to fully autosize the system.

I need the AHU to control moisture ratios only (as the terminal 
reheat boxes will take care of temperature). Unfortunately, I am 
experiencing the cooling coil always being turned on along with the 
humidifier. Therefore, during the winter months, I have the cooling 
coil being turned on for no reason. 
	
The one thing I have noticed that the when I look at the `System 
Node Humidity Ratio Max' for the cooling coil's control node, the 
values are set to `0' during the winter months. I think this may be 
causing the cooling coil to attempt to strip 100% of the moisture 
from the air. I may be wrong, but I can't think of any other reason 
for this. Under normal circumstances, I would turn off the cooling 
coil in the winter months, however, due to the tight RH control, I 
need to keep it on for the year-round simulations.

I've uploaded the file (called 'Tight RH Control Problem') but I've 
also included the objects that may be of relevance. Once again, I 
would really appreciate people's input.

SET POINT MANAGER:SINGLE ZONE MIN HUM,
    zThirdCloseControl Min Hum Manager,  !- Name
    ,                        !- Control variable
    ,                        !- Schedule name
    AHU3 Humidifier Outlet Node,  !- Name of the set point Node or 
Node List
    zThirdCloseControl Node; !- Name of a Node List (or Node)


SET POINT MANAGER:SINGLE ZONE MAX HUM,
    zThirdMediaRoom Max Hum Manager,  !- Name
    ,                        !- Control variable
    ,                        !- Schedule name
    AHU3 CC Outlet Node,     !- Name of the set point Node or Node 
List
    zThirdCloseControl Node; !- Control zone air node name


CONTROLLER:SIMPLE,
    AHU3 Cooling Coil Controller,  !- Name
    TEMPandHUMRAT,           !- Control variable
    REVERSE,                 !- Action
    FLOW,                    !- Actuator variable
    AHU3 CC Outlet Node,     !- Control_Node
    AHU3 CC Water Inlet Node,!- Actuator_Node
    0.001,                   !- Controller Convergence Tolerance: 
delta temp from setpoint temp {deltaC}
    autosize,                !- Max Actuated Flow {m3/s}
    0;                       !- Min Actuated Flow {m3/s}

ZONE SIZING,
    zThirdMediaRoom,         !- Name of a zone
    18,                      !- Zone cooling design supply air 
temperature {C}
    28,                      !- Zone heating design supply air 
temperature {C}
    0.00777,                 !- Zone cooling design supply air 
humidity ratio {kg-H2O/kg-air}
    0.0083,                 !- Zone heating design supply air 
humidity ratio {kg-H2O/kg-air}
    flow/person,             !- outside air method
    0.00944,                 !- outside air flow per person {m3/s}
    ,                        !- outside air flow per zone {m3/s}
    1.2,                     !- zone sizing factor
    design day,              !- cooling design air flow method
    ,                        !- cooling design air flow rate {m3/s}
    design day,              !- heating design air flow method
    ;                        !- heating design air flow rate {m3/s}


SYSTEM SIZING,
    AHU3 Air Loop,           !- name of an AIR PRIMARY LOOP object
    total,                   !- type of load to size on
    autosize,                !- Design (minimum) outside air 
volumetric flow rate {m3/s}
    1,                       !- minimum system air flow ratio
    3,                       !- Preheat design set temperature {C}
    9,                       !- Central cooling design supply air 
temperature {C}
    16,                       !- Central heating design supply air 
temperature {C}
    noncoincident,           !- Sizing Option
    no,                      !- Cooling 100% Outside Air
    no,                      !- Heating 100% Outside Air
    0.00777,                 !- Central cooling design supply air 
humidity ratio {kg-H2O/kg-air}
    0.00783,                 !- Central heating design supply air 
humidity ratio {kg-H2O/kg-air}
    design day,              !- cooling design air flow method
    ,                        !- cooling design air flow rate {m3/s}
    design day,              !- heating design air flow method
    ;                        !- heating design air flow rate {m3/s}

Kind regards

-Elmer








------------------------ Yahoo! Groups Sponsor --------------------~--> 
You can search right from your browser? It's easy and it's free.  See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/