You are correct in your interpretation of the equations used for each
report variable. The difference in these variables is that the Heat
Exchanger Total Heating/Cooling Rate refers to the energy transfer of
the heat exchanger (supply air outlet - supply air inlet). The Stand
Alone ERV Zone Total Heating/Cooling Rate refers to the energy transfer
to the zone (supply air outlet - exhaust air inlet). In winter the HX
will usually heat the entering outdoor air but the system effect on the
zone is cooling. In summer this is reversed. The zone meters record each
of these report variables for the entire simulation period.
eric_zhou1223 wrote:
> Hi all,
>
> I notice there are variables following below when I run the ERV
> modules:
>
> HVAC,Average,Heat Exchanger Total Heating Rate[W]
> HVAC,Average,Heat Exchanger Total Cooling Rate[W]
> HVAC,Average,Stand Alone ERV Zone Total Heating Rate[W]
> HVAC,Average,Stand Alone ERV Zone Total Cooling Rate[W]
>
> Does the "HVAC,Average,Heat Exchanger Total Heating/cooling Rate[W]"
> refer to Q_total for heat exchanger on Page 541(equation 479) in
> EngineeringReference.pdf(ver 1.30), while the "HVAC,Average,Stand
> Alone ERV Zone Total Heating/Cooling Rate[W]" refer to Q_total for
> ERV on Page 683?
>
> What is the difference between the Q_ERV and Q_HEX ?
>
> I guess the two heat transfer happen in sequence: first the Q_HEX
> and the air outlet condition is found; and then the Q_ERV come into
> being to the zones..
>
> Next,the "Zone,Meter,HeatRecoveryForHeating:EnergyTransfer [J]"
> finally accumulates the ""HVAC,Average,Heat Exchanger Total
> Heating/cooling Rate[W]"".
>
> Is my knowledge right?
>
> Thank you.
> Eric
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/2pRQfA/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/