[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Outputs
> outside air I still would have the zone/sys sensible load to cooling setpoint
> reporting me the cooling coil sensible load only? I mean, does this variable
> report only the load when the coil is on?
No. The predicted load is the load required to meet setpoint after all non-
HVAC loads have been accounted for (which includes VENTILATION). If the HVAC
system (in this case purhcased air) is providing the outside air, then the
outside air becomes a load internal to the system and not a load in the zone.
Draw a boundary at the HVAC system inlet to the zone:
Zone/Sys Sensible Load to Cooling Setpoint Predicted [W] is the rate of cooling
that must enter the zone at this point to meet setpoint.
Zone/Sys Sensible Cooling Rate [W] is the rate of cooling the system actually
provided to the zone.
If these values agree, then setpoint is met. If these values are different,
then the zone temperature will be different from the setpoint.
Regarding the outside air option in purchased air. Do not use it. PURCHASED
AIR is a variable volume device at a constant supply air temperature. It
cannot and will not introduce unconditioned fresh air to the zone. If the zone
load is small, the total volume delivered may fall below the outside air flow
rate. This will reduce the outside air flow rate and a warning will be issued.
For any situation other than peak loads where the total supply volume will be
greater than the outside air volume, the outside air option in purchased air
should not be used.
Mike
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/