[EnergyPlus_Support] Sizing calculation
Hi,
I am performing system sizing calculations for a 3-zone building
where only one of the zones is conditioned.
*Temperature control is provided with a dual setpoint thermostat.
*The selected unitary equipment object
is "FURNACE:BLOWTHRU:HEATCOOL".
*The following parameters are set the same on both the Zone and
System levels:Cooling/Heating Air Flow Methods, Cooling/Heating
Supply Air HR, and Cooling/Heating.
*The HVAC unit performance parameters are set to "Autosize" when
ever that option is applicable.
With this input, the sizing routine comes up with a max flow rate
that meets the heating but not the cooling setpoint temperature.
When I manually increase the design cooling flow rate value in the
SYSTEM SIZING and ZONE SIZING objects, all setpoint temperatures are
satisfied.
I am trying to understand why the "sizing" routine was limited to
meeting only the heating setpoint temperature. Please provide help
when you have a chance.
Thank you for your valuable time.
Merid
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/