Re: [EnergyPlus_Support] Sizing calculation
It is difficult to say for sure without seeing the input file. The most likely
cause is that the cooling supply air temperature in the ZONE SIZING object is
colder than what the DX cooling system can actually produce. If that is not
the problem, then I would need to see the input file. You may upload it to the
files area of the yahoo group, or e-mail it as a zipped attachment to
energyplus-support@xxxxxxxx
Mike
On 4 Oct 2006 at 20:32, aboyemeplus wrote:
> Hi,
>
> I am performing system sizing calculations for a 3-zone building
> where only one of the zones is conditioned.
>
> *Temperature control is provided with a dual setpoint thermostat.
> *The selected unitary equipment object
> is "FURNACE:BLOWTHRU:HEATCOOL".
> *The following parameters are set the same on both the Zone and
> System levels:Cooling/Heating Air Flow Methods, Cooling/Heating
> Supply Air HR, and Cooling/Heating.
> *The HVAC unit performance parameters are set to "Autosize" when
> ever that option is applicable.
>
> With this input, the sizing routine comes up with a max flow rate
> that meets the heating but not the cooling setpoint temperature.
> When I manually increase the design cooling flow rate value in the
> SYSTEM SIZING and ZONE SIZING objects, all setpoint temperatures are
> satisfied.
>
> I am trying to understand why the "sizing" routine was limited to
> meeting only the heating setpoint temperature. Please provide help
> when you have a chance.
>
> Thank you for your valuable time.
>
> Merid
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/